    PV array voltage significantly higher than expected

    I have 10 more panels not installed. I also have a second charge controller. Sadly that circuit has a 10amp DC rated breaker on it already as I was only anticipating 5.2amp max through that circuit in its current configuration. I have some options though. I wanted to keep the voltage high...
  2. D

    PV array voltage significantly higher than expected

    It's only a red alert when we approach -40F!
  3. D

    PV array voltage significantly higher than expected

    I was multiplying Vmc to the temp differential times the number of panels and keeping that value below 450vdc which it is. In reality though I want to multiply Voc times the temp differential times the number of panels and keep that voltage below 450vdc instead of 500vdc. Now it makes sense.
  4. D

    PV array voltage significantly higher than expected

    Ok, So what is really want then is to use Voc multiplied by the temp differential at -40C/-40F multiplied by the number of panels and keep that value below 450vdc not 500vdc to be safe.
  5. D

    PV array voltage significantly higher than expected

    Ok this makes sense. Sort of. Is it likely that above 450vdc the mppt controller shuts off like it does below 120vdc?
  6. D

    PV array voltage significantly higher than expected

    I don't know! I'm asking you! I'm not doubting your logic, but if we use that the VOC and max PV array voltage should be the same value no?
  7. D

    PV array voltage significantly higher than expected

    https://signaturesolar.com/eg4-3kw-off-grid-inverter-3000ehv-48/
  8. D

    PV array voltage significantly higher than expected

    Ok, the EG4 manaul says Max PV array open circuit: 500vdc PV array: 120vdc-450dvc It's not clear why the voc and array max voltages are different then.
  9. D

    PV array voltage significantly higher than expected

    That's open circuit voltage. I'm not measuring open circuit voltage. I'm measuring the voltage with a load connected.
  10. D

    PV array voltage significantly higher than expected

    18x Renogy 100w panels wired in series 24.3voc per panel 20.4vmp @ 25C voltage temp coefficient -0.28%/C current outside temp +12F/-11C coefficient 0.28x36 = 10.08% panel voltage 22.45v at -11C string voltage 404vdc at -11C also string voltage 434vdc at -40F/-40C which is what I spec'd for as...
  11. D

    Need help choosing 48v all-in-one

    I have a current shunt to measure SoC for all charging sources and loads. I'm not sure if the 3kw EG4 can track SoC using non-EG4 batteries as I'm using the LiTime 230ah 12v 4x in series. Thanks again for your helpful advice!
  12. D

    Need help choosing 48v all-in-one

    I'm at 65.5 degrees north latitude.
  13. D

    Need help choosing 48v all-in-one

    I want to setup 3 pv arrays. A main array that will be pointing due south wired into my EG4. I want to setup two additional arrays: One facing due east and the other facing due west. Are there any issues wiring the east/west arrays in parallel (each array will be the same number of identical...
  14. D

    LiTime 12v battery showing 18.0v resting

    I had already wired them and had the charger on them before I saw your reply. I was able to charge at the 50A setting. The voltage started at about 13.5V and rose steadily. In less than an hour it made a sudden voltage jump, and then a second one. After that the clamp meter showed zero...
  15. D

    LiTime 12v battery showing 18.0v resting

    No I have not. Thank you for the further clarification. I can wire them in parallel and charge them but I can't use the EG4 since it only supports 48v sized batteries. I do have the "dumb" 12v charger but I cannot control the voltage output only the current. Again it's the style of charger...