  1. D

    Planning a Backup solar system for my Main solar system! Any ideas welcome

    When I see it now, I think I would like everything except the EG4s working as a backup with a manual or automatic switch, if possible. There are 2 battery racks of 6 EG4 48 Volt/100Ah each. 6 x EG4 LL 6 x EG4 LifePower
  2. D

    Planning a Backup solar system for my Main solar system! Any ideas welcome

    I add a drawing of the situation. The Generac generator is connected also to a switch, so that the Growatt can get either power from the generator or from the duel fuel mobil generator.
  3. D

    Planning a Backup solar system for my Main solar system! Any ideas welcome

    So the AC input of the EG4 would handle the AC output of the Growatt? I kinda like this idea, when it works.
  4. D

    Planning a Backup solar system for my Main solar system! Any ideas welcome

    Sometimes you could run into a situation (having air bnb guests, open gatherings) where you might be lucky, when a completely separate solar system provides you instant power. Also, when a EG4 unit fails, has to be repaired and I can't get a quick fix. So I am more thinking of backup system than...
  5. D

    Planning a Backup solar system for my Main solar system! Any ideas welcome

    Since I am planning to setup two buildings (cottage and workshop) with solar panels, I am running into a challenge, how to provide maximum PV input to my 2 x EG4 18kpv (not yet connected) in parallel as well as my already existing Growatt 12 kW with 24 x 300 W Canadian Solar panels in 4s3p mode...
  6. D

    Generac Eco-Gen 15kW (2020) to Growatt 12kW -> 2-wire-start-stop dry contact problem

    Seems I just have to be patient and wait until the battery hits the setting to let the generator kick in. Hasn't happened yet, but the system runs without any issues.
  7. D

    Generac Eco-Gen 15kW (2020) to Growatt 12kW -> 2-wire-start-stop dry contact problem

    Thanks for sending this information. I will double check that. The generator was hooked to a magnum solar system since 2 days ago and worked just fine. So I might think, that it should not be a generator issue. The crazy situation is, that the Growatt doesn't seem to send different signals...
  8. D

    Generac Eco-Gen 15kW (2020) to Growatt 12kW -> 2-wire-start-stop dry contact problem

    I talked to Signature Solar today (where I bought the Growatt), but they couldn't help me with the situation. Still the dry contact in the Growatt stays open, no matter, what setting I choose. When I close the two contacts manually, Generator starts instantly. There is no voltage on the...
  9. D

    Generac Eco-Gen 15kW (2020) to Growatt 12kW -> 2-wire-start-stop dry contact problem

    I hooked up my generac, which has the 2 wire start stop, to my Growatt 12kW with the dry contact (NC and C are connected to the wires) but for some reason the generator doesn't start after I drained the EG4-LL batteries a little to have the possibility to test the automatic switch function with...
  10. D

    Four EG4 6500EX in split phase - Fault 80 Question

    I completely agree. There must be a reason, why signatur solar runs this hidden recall program for these inverters: Upgrade program I will try my best but I need a fast solution, otherwise I continue burning money through the roof, while using the generator 10 hours per day. There seems to be a...
  11. D

    Four EG4 6500EX in split phase - Fault 80 Question

    Yes, main thing seams to be the update of the firmware. I will first install the new firmware on all devices tomorrow and see what happens. I'm not sure whether both cables (positive and negative) of the parallel installation of 2 battery racks, which are connected to an extra bus bar, are only...
  12. D

    Four EG4 6500EX in split phase - Fault 80 Question

    Hi, I am new to this forum, have looked around but could find anything about the fault 80 in combination with the EG4 6500EX. I have a split phase setup with 4 x EG4 6500EX inverters, first 2 with a load center as Line 1 and second 2 with a load center as Line 2. First and second inverter set...