I am a bit lost with the difference between the DC input range and the full-power MPPT voltage range. If I understand, the 18Kpv can support intake voltage from an array up to 600 volts.
The worst-case scenario brings me within 19 volts of max. What is the consensus?
Total string OC voltage: 450.09
Nominal maximum power: : 4050
Worst case temperature: -1.1
Temperature coefficient (Voc): -0.27
Temperature coefficient (Pmax): -0.34
For these, your:
Total worst case...
I have 24 panels at the moment, the space where they are installed can handle 30. Is it possible to run 10 panels on mppt 1 and mppt 2 and the remaining 4 on mppt 3 until the other 6 panels are sourced? The manual suggests all 3 strings need to have the same amount of panels. Please advise.
10...
The EG4 18kv will live In the carport, 170 feet away from the critical loads panel it will feed. The subpanel will have a 70-amp (80-amp if possible) main breaker. Do I need #2AWG or would #4 AWG for the approx 170tf run? A bit confused on whether the max voltage drop of 3% is for continuous only.
NEC dictates DC circuits are to be in metal conduits within a structure. The IMO DC disconnect is Plastic/pvc, do I need to install these inside a metal enclosure?
I planned to mount 3 DC disconnects on top of a metal enclosure using chase nipples. Run my PV wire to the metal enclosure via a...
At that point, we were discussing liquidtight Flxible MC. The run from the roof to where it goes into the structure is 10ft. Four feet on the roof and about another 4 feet down the wall.