diy solar

diy solar

Most reacted posts

  • Post in thread: Looking for guidance on liquid cooling home

    I agree, I am dedicating the size of a two car garage for the equipment room and storage tank. Fortunately, land and bricks are cheap as chips here. My calculations are roughly 1,000 L of -50 C liquid to maintain 22 C over 12 hours for a 2,000 square foot house. I am configuring at least three...
  • Post in thread: Growatt grid-tied connection time issue

    Hopefully, it is possible to reconfigure in the software. However, if it is not, you could consider a little DIN rail/MCB box with a three minute delay timer (upon power on) and a contactor.
  • Post in thread: Growatt grid-tied connection time issue

    2.5 kV !?
  • Post in thread: Transformer location

    There are better ways to do this without messing with the utility. Put a relay, contactor or ATS of sorts between the appliances you want to power (e.g. office circuit, hot water tank, washing machine, microwave circuits) and the micro inverter. That way, you are doing it more safely and without...
  • Post in thread: Three phase 100 KW Inverter recommendation

    Hello, I am looking for an off-grid inverter recommendation for 100 kW with a specific voltage of 440Y/254 V. 50 Hz is preferred, though we can also work with 60. I am using hundreds of 350 W panels, so I can configure the wiring of the panels as is best for the inverter. Thanks in advance!
  • Post in thread: SolarEdge SE100K-US

    You are absolutely right. Although exporting to the grid in the future would be a nice option to have, it is not the initial engineering plan. I am currently considering two SOL-ARK 60K-3P-480V inverters (https://www.sol-ark.com/sol-ark-60k-3p-480v-n/) in parallel, based on recommendations. I...
  • Post in thread: Three phase 100 KW Inverter recommendation

    I will take a look at Sol-ark, thanks for the suggestion. I found the model here: https://www.sol-ark.com/sol-ark-60k-3p-480v-n/. They even have a specs sheet in Español. :) I am curious to consider running multiple inverters as separate systems as well, depending on the capacities; i.e. one or...
  • Post in thread: Three phase 100 KW Inverter recommendation

    This is what I've found on the Sol-ark voltage selection. Do you guys have any more insight with those particular style of inverters? Update: I have a request out to the Sol-ark engineering team. I will post when I hear back!
  • Post in thread: feed inverter from grid

    You could need an isolation transformer (two in open wye/delta or three) to avoid troubles. A more custom transformer could also act as current shunt (similar to neon sign transformers with limited current). However, it may be more cost effective to accomplish this with buck boost circuity...
  • Post in thread: Flywheel Energy Storage

    I would probably want to bury the system in an underground vault if more than a coupe kWh... That is an excessive amount of kinetic energy. I was about to open a new thread with this exact subject, but I see it is already being discussed. I am looking into flywheel energy storage for my...
  • Post in thread: Super capacitor storage

    I have been very impressed with super capacitors in my electrical engineering experience. I would like to explore the cost effectiveness of building a super capacitor bank for energy storage to use at night time, especially considering the costs of these components from overseas is decreasing as...
  • Post in thread: 208 system in Mexico

    A side note; something cool about having the neutral in a three wire 208Y/120 or 220Y/127 V service is that you can derive a system with the missing phase to properly drive three phase equipment if you ever need to. I.e. by using an open-wye open-delta transformer setup: or
  • Post in thread: Inverter with higher voltage

    Hello, I am looking for an inverter or series of inverters that can be combined to output 440Y/254 V 50 Hz at 100 kW (~33 kW per phase). I am having a hard time finding this. I was in discussion with Gro-watt about custom firmware, but the communication went dead. Is there a way to override...
  • Post in thread: SolarEdge SE100K-US

    Is the nominal voltage field programmable on the SolarEdge SE100K-US? We are looking for a similar set of inverters, with a target voltage of ~ 440Y/254 V. This inverter will be completely off grid (no connection to grid in sight), with critical loads downstream using an ATS to generator before...
  • Post in thread: Three phase 100 KW Inverter recommendation

    I was looking at the SolarEdge SE100K-US, (480Y/277 V) but I am not sure that its voltage will be adjustable and I would not want to budget extra for buck boost transformers if there is an inverter that can put out exactly what we need. I am diverging a bit from a typical setup, specifically...
  • Post in thread: Gro-watt firmware

    Hello, Would you guys please send your Growatt firmware ".bin" files to me if you happen to have any available? I am a software developer thinking of purchasing some Growatt inverter, but I want to check whether it is possible to change my custom EPS voltage requirements. Thank you
  • Post in thread: Crazy things you do with excess power

    Perhaps export to the grid, or boil the the ocean.
  • Post in thread: Inverter with higher voltage

    I was looking at the manual of the CSI-100K-T400, but I am not clear whether it has off-grid functionality and the precisely adjustable voltage. If you have any experience with this line of units, please let me know...
  • Post in thread: Looking for guidance on liquid cooling home

    I am calculating how much more would be required. What do you think? The cost of the 1,000 L tanks is also a factor to consider, whereas investing that money in additional solar panels for a more powerful compressor could mean having surplus power down the road that can be more useful (e.g. sold...
  • Post in thread: Looking for guidance on liquid cooling home

    I am looking to engineer a system that maintains and stores 1,000 L of a glycol/water mixture at -50 C during the day. My calculations are that it is more economic to store a large volume of cold liquid rather than buying the batteries to compress on demand in the night time. I also have an...
  • Post in thread: Possible to use Sol Ark Gen terminals with a 3 Phase Generator ? Sol Ark techs said NO !

    If you want a transformer, you could use 208:240 V split phase or a Scott-T transformer to better balance the load. Many three phase generators are reconfigurable to split phase, if there are enough poles/winding taps to do so on yours.
  • Post in thread: SolarEdge SE100K-US

    Update: I have been told that these are the three available off-grid configurations: Perhaps there is an aftermarket way to hack it if I can gain access to the configuration files or flash with custom firmware? Does anyone have any suggestions for a different set of inverters that can reach...
  • Post in thread: 208 system in Mexico

    How many meters are you allowed to have - one per structure or address? So you could subdivide your own property to get more meters, in theory?
  • Post in thread: Super capacitor storage

    OK, I think that arithmetic nips it in the bud. Thanks for that. The only use case I can comprehend is perhaps a small bank to handle the brief surge demand of power through an inverter for things like motors or heaters starting up.
  • Post in thread: Grounding and Starlink

    If you want to eliminate any possibility, you could set up a couple panels with DC charge controller near the satellite modem and use an ethernet-fiber media converter on both sides. The fiber will be non-conductive. A reasonable enough path is to use Ethernet surge suppression on both sides...
  • Post in thread: Looking for guidance on liquid cooling home

    Thanks for confirming that, this ratio lines up with my previous research. I think for sure filling the tank with mostly gravel could work well. This idea is resonating with me quite well. Water is free for me, but the propylene glycol is a bit inconvenient for the initial set up otherwise. Do...
Back
Top