  1. ns31

    UK inverter breaker sizes and tails

    Racking my brains I think I've figured this out. At 40a, the inverter would only require a 10-16mm cable, should more than 7.5kw be required, a second inverter also has it own an rcbo on a 10-16mm cable. The AC outs of the inverters then combine at a parralel box, this box then has 25mm tails to...
  2. ns31

    UK inverter breaker sizes and tails

    Hi all, I'm confused about grid connection breakers with inverters (in hybrid or off grid) and the AC input/ grid connection. Taking a 7.5kw solax inverter for example, the max AC input is 40a. Therefore, a 50a breaker in the consumer unit would be suitable, but my confusion is mostly around...
  3. ns31

    Inverter upgrade from MPP solar 11kw

    I went with the SolaX 7.5kW G4 Hybrid Inverter in the end, will probably get two of them longer term. Going to switch to their HV battery system which looks amazing (it can go outdoors so no fires for me!), and they're releasing as new S36 battery next month so I'll go with that one. Very...
  4. ns31

    Reliable PV DC disconnect?

    It arrived, it's a lovely piece of kit. I usually figure out wiring with a combination of a multimeter, and the instructions, but can I just sanity check something that appears to be a confusion in the design?... The terminals on the top appear to be indicated with a negative symbol. Yet this...
  5. ns31

    Inverter upgrade from MPP solar 11kw

    Yes they look really good too, but I'd prefer >550v pv voltage if possible
  6. ns31

    Inverter upgrade from MPP solar 11kw

    Sadly its grid tied. I'm looking at the SolaX 7.5kW G4 Hybrid Inverter. Trying to figure out how to plug in us5000 cables before ordering but it looks like a decent spec
  7. ns31

    Inverter upgrade from MPP solar 11kw

    Annoyingly the Solis Hybrid inverter is 6kw max it seems, they look like decent inverters otherwise
  8. ns31

    Reliable PV DC disconnect?

    Thanks. Each string is 446.76v as the voc is 37.23v and there's 12 panels per string. Do IMO offer a product that will handle 2x strings at this rating? I'm assuming it needs to be >1000V rated
  9. ns31

    Inverter upgrade from MPP solar 11kw

    Hi all! I installed an 11kw Off grid system using an MPP solar 11kw Max inverter and 24x JA Solar 405w panels (in 2x strings of 12), it was a nice starting point and works well, only I would now like to build upon what I've learned and start to improve the quality a little. I'd like to replace...
  10. ns31

    Reliable PV DC disconnect?

    Can I just check, is the following 600V per series string? So 1200V in total? https://www.solartradesales.co.uk/imo-dc-isolator-25a-4-pole-600v-two-strings
  11. ns31

    Reliable PV DC disconnect?

    Just what I was looking for thank you
  12. ns31

    Reliable PV DC disconnect?

    Interesting this, I'm assuming the PV disconnects can be quicker and built with arcs in mind?
  13. ns31

    Reliable PV DC disconnect?

    Hi all, I wired up 2x strings to a DC disconnect made by Dihool (Chinese)... https://www.amazon.co.uk/Isolator-Disconnect-pre-wired-connectors-Waterproof/dp/B0B8YRBHHZ/ However, I'm aware that the cheap brands of DC disconnect increase the risk of fire. Even if the fire risk is low I'd like to...
  14. ns31

    Max PV for inverters

    Is this common to all inverters? Hybrid and offgrid? It makes sense that the inverters are bypassed (e.g. a 3kw inverter would often require bypassing), but I wanted to make sure that's how they operate, rather than shutting down with an overload warning.
  15. ns31

    Max PV for inverters

    So if I used an 8kw off grid all in one inverter (with an AC/grid input), and had that connected to a CU which powered a 9kw device for example, would the inverter produce 8kw and then take the extra 1kw from the grid/AC? Or would it overload?