  • Post in thread: 11kw Generac Guardian 2-Wire Start Behavior - Confusion

    Thank you for the reply. Originally I thought setting up the Stand-by generator would be similar to what you just described. But for Generac stand-by Generators, the ATS is tied dependent on the signal from the generator’s controller. It is the controller that does the Utility Sensing...
  • Post in thread: Anyone have the scoop on the upcoming Sol-Ark limitless system?

    Found this thread becasue I was researching the 12K and this new 15K, if as described by the specs, will be perfect! Exactly what I need. Even though a 12K should be OK, I don't want to use a critical loads panel. My house is in concrete and adding that can be a daunting and messy task. The...
  • Post in thread: Sol Ark 12k Off Grid with small generator - peak shaving

    Hello All! I just spoke with a rep from Sol-Ark. The person confirmed that indeed, Gen Limit Power uses the Inverter's internal sensors to limit the incoming power from the GEN INPUT. (I asked them to clarify this on a next revision of the manual) You then configure the Charge under Batt...
  • Post in thread: 11kw Generac Guardian 2-Wire Start Behavior - Confusion

    Update Installed a small switch for the Trasnfer signal wire. Tested the Gen Start function from the SolArk and it worked as expected, the ATS did not transfer. Now if the SolArk for some reason goes out of service. All I need to do is flip de signal switch back ON, disable the remote start...
  • Post in thread: 11kw Generac Guardian 2-Wire Start Behavior - Confusion

    Hello All, As stated in the title, I have an 11kw Generac Guardian with the Evolution controller (bought in 2015) and a 200 AMP Automatic Transfer Switch (model: RTSR200A3 ). I now have a SolArk 12k with a small battery bank - 9.6kwh. I finished doing the connection for the 2-wire remote...
  • Post in thread: Sol Ark 12k Off Grid with small generator - peak shaving

    Hello All I was just looking into this and stumbled upon this thread. Incredible that SolArk themselves are not clear on the function of the "Gen Limit Power" setting. Wow! My current system uses a 12K-P (outdoor) and 12kw in PV. It currently does not have a battery bank. It is a grid tied...