Having difficulty discerning NEC Table 690.31(A)(3)(1).
I am planning on 2 MI solar branches (20 feet apart) running 12 AWG Enphase Q cable to 8AWG THWN-2 (2 CCC each branch) via PVC sch 80 above grade then to sch 40 at 18" below grade to a pull point where they will be joined (4 CCC in one...
I am centerfeeding a string of 16 M215 Enphase Miroinverters (so the junction box is in the middle of 2 sets of 8 MI). Altogether this would be 16 MI that would land on the breaker in the Enphase Combiner box and I am wondering if this should be 20A or 30A.
The current per MI is 0.9 so 16* 0.9...
I bought 34 M215 Enphase Microinverters on ebay about 6 months ago. The Engage cable that came with it has 10 connections of which are landscape - the 24 other connections are portrait.
However I need to have 32 landscape length connections. How would you fix this?
Buying options for Engage...
Hi wizards, very thankful for all of the wisdom in this community. I live in an area where we do not see too many solar installs. Initally we were going to use a solar installer but communication delays won out - so DIY is the way. I am preparing to submit plans to inspection office.
How...