IIRC i got the full 65W charge rate up to 97% SOC and for sure was getting it below 95% SOC
What is your solar voltage under load? I bet its saging quite a bit.
If you can get your Voc, Isc, Voltage under load, and current under load
As Bob142 said it could be a bad adapter cable, try...
What is your Locked Rotor Amperage? Running watts vs Starting (LRA) watts
It is usually 2-3x your running watts so your fridge may pull up to 2484w for 2-3 seconds before the compressor starts turning
Yes just a residence, the 23A is locked rotor as if the pump was siezed, starting surge will be less than that.
Full load nameplate is 5A@230v so a 3x surge is less than 4kw
Im mostly just looking whats out there thats more cost effective or has more features than mpp solar
I just noticed this today, however i was only getting 65w out of a rich solar 100w panel, both brand new and 75% soc, about noon on a clear day i wonder if thats the PWM controller thats hamstringing it or being flat mounted
While their is enough sun to effectively overpanel the needs of both units i would expect them to charge at max rate in paralell just fine, once the sun starts to drop is where it would get interesting as i would expect a pair of MPPT controllers to start fighting to maintain their own power...
Search, Option 1, Option 2, Option 3
My continous draw will be 25-28A so im guessing ill need a 30A+ BMS and i need it to be one of the smart ones since im not sure how close to 16v the small PSW inverters will so i want to set the overcharge cutoff at 3.95v or where needed
Thanks guys
-squoril
uncle wants to put in solar to run his well pump and im trying to give him a DIY estimate
He has a 230v 1/2hp pump which is on a 15A breaker and has a locked rotor draw of 23A, based on 15*230 im thinking a 4kva rated inverter will run the pump and im curious whats out there price wise
right...