Help with external Battery bank disconnect inspection required

MikeSpeegle

New Member
Joined
Sep 13, 2023
Messages
62
Location
Crowley, Texas
I just got flagged needing a radio freq or remote battery disconnect for me 4P4S 16x12.8v 250ah setup that is in my garage. Any thoughts besides running 4/0 to outside of house?
 

Attachments

  • IMG_0981.jpeg
    IMG_0981.jpeg
    311.7 KB · Views: 28
  • IMG_0978.jpeg
    IMG_0978.jpeg
    210.7 KB · Views: 28
  • IMG_0979.jpeg
    IMG_0979.jpeg
    243.9 KB · Views: 28
  • IMG_0980.jpeg
    IMG_0980.jpeg
    271.3 KB · Views: 27
How does this work? If I read correctly it’s 36v 500 amp. I need 48v and 400-500 amp. Will it work with 48v
"Contact Voltage" is 12-900v. "Contact Current" is 500a.

The "Coil Voltage" is 9-36, 32-95v, 48-95v volts, depending upon the model. This is the voltage that controls the coil to open or close the Contact. So, you can have a 12v line to an outside switch as a control line. You can get the 32-95v model to run the control line at battery voltage, but then you have more rules you have to follow for the wire protection.

 
Last edited:
"Contact Voltage" is 12-900v. "Contact Current" is 500a.

The "Coil Voltage" is 9-36, 32-95v, 48-95v volts, depending upon the model. This is the voltage that controls the coil to open or close the Contact. So, you can have a 12v line to an outside switch as a control line. You can get the 32-95v model to run the control line at battery voltage, but then you have more rules you have to follow for the wire protection.


Ok thank you very much. I will order one. Will the documentation tell me what external coil economizer I will need?
 
Any thoughts on Blue Sea’s option it has no continuous current and only uses power in switching 12v 7amp for 40ms.


It’s not UL certified but it’s Marine certified SAE & ISO. Will I have an issue with that?

Thanks again
 

Attachments

  • IMG_1080.jpeg
    IMG_1080.jpeg
    99.6 KB · Views: 1
I don't think you need ul listing for 12v. I would get an outdoor rated case, and put a big "stop" button inside. Make it easy for the fire fighter, and a protection against a tree branch hitting it.
 
I don't think you need ul listing for 12v. I would get an outdoor rated case, and put a big "stop" button inside. Make it easy for the fire fighter, and a protection against a tree branch hitting it.
How about this? In reality it’s barely larger than single gain outlet. Also thank you!!!

Also the feed is only 12v but the battery bank is 51.2v 1,000ah
 

Attachments

  • IMG_1085.jpeg
    IMG_1085.jpeg
    64.6 KB · Views: 5
Last edited:
Your local jurisdiction must be requiring the latest spec which involves estop or outdoor accessible battery shutoff (in addition to remote service disconnect etc). For example the eg4 llv2 "S" version batteries where the circuit breakers can be triggered via a shunt if commanded by a communicating inverters rsd button.
 
You need UL listing in most localities in U.S. if unit is grid interconnected.

You should not need to physically disconnect batteries, other than a normal manual inside structure breaker. You do need an inverter emergency remote shutdown button/switch put outside with proper labelling for firefighting service.

Before you consider those relays you should look up how much current their engagement coil takes. They are usually intended for intermittent service (like running a starter motor or winch) and when left on for long period of time their coil gets very hot.

You can get latching relays. It only consumes coil power long enough to push contact to on or off. This is the type of switches used for generator backup transfer switches.
 
Midnite solar made the "birdhouse" for this but it looks like they discontinued making it?
 
Midnite solar made the "birdhouse" for this but it looks like they discontinued making it?
I think that just covers disconnecting the PV circuits so firefighters can walk the roof without hazards.

You could use a remote triggered midnite 125V 250A breaker with outdoor switch but don't know about UL listing etc and you'd be limited to around 250A.
 