While we are concerning ourselves with wire and bus bar resistance and the potential voltage differences . . .

00 AWG copper has a resistance of approximately 0.079 ohms/1000 feet.​
My 33 inch battery lead wires (call it 3 feet) have a resistance of . . . 0.079/1000 x 3 = 0.000237 ohms​
@ 100 amps current (per battery) the expected voltage drop across the wires would be . . . 0.000237 ohms x 100 amps = 0.0237 volts.​
Figuring voltage drop across both the + and - leads . . . 2 x 0.0237 = 0.0474 volts​
Of the several boats that I've owned over the years, this boat has the largest size wiring of all of them. I think my other boats had only 2 AWG wiring by comparison.
 
There is one additional consideration that the installation manual makes note of in larger battery arrays (4P, etc), is to join the batteries together for balancing. They don't show it in the simple 2 parallel installation, but it still could apply, because it is one of the preparation steps outlined in the manual.

  1. Fully charge each battery to the same resting voltage.
  2. Connect the batteries together in parallel and let rest for 12-24 hours.
I could add a wire between the batteries (updated picture below), but I'm assuming they will tend to balance any way by virtue of their common connection at the bus bar.

FWIW - the battery cables are 2/0 (00) AWG with crimped and soldered connections each are 33" in length. I believe they are/were sized by the boat manufacturer for 100+ amps, based on the typical runs to the main power-consuming components in the boat. (Inverter, Engines, windlass, etc)

The most power consuming component on the boat is the 2000 watt inverter, which (theoretically) could draw about 165 amps at full load. The most I've seen it draw on a single load is 40 amps (powering the air conditioner). I have a small microwave oven that needs about 1000 watts to run, but the inverter won't run it unless it has 120 VAC shore power connected. I assume the microwave would need upwards of 100 amps into the inverter to generate the 1000 watts @ 120 VAC that it needs.



If you are going to bridge(?) the batteries, this an the accepted method and it wont matter which end of the buss bar you connect to:
24vBatteryConnection4.JPG
And it's important to make sure the lengh between the positives and the length between the negatives is the same as closely as possible. If you are connecting them directly to the buss bar, the negatives all need to be the same length to their buss and the positives the same length to their buss as shown in the original diagram in the book.

Let me see if this makes sense: If you lay out the batteries in a north south pattern (2 or more batteries) and the Neg is on the west and the Pos is on the east, then you want all the Neg cables to the buss bar the same length and all the Pos cables to their buss bar the same length. NOW HERE IS THE THING THAT GETS MISSED: If you connect the System Neg to the North end of the Neg Buss, you want to connect the System Pos the the SOUTH end of the Pos Buss. If you connect both the north end, the battery that is on the north end will degrade fastest. Electricity wants to follow the path of least resistant which is usually the shortest distance. The batteries farthest from the load will get the least "use" in the circut.

If you watch Will's videos where he installs multiple rack batteries, he specifies that if you connect the Neg to the bottom of its buss, you connect the Pos the TOP of its buss (or viceverse) . I've been changing out battery packs in large server rack UPS' for 20+ years and had completely missed that they were wired like that (thankfully I was only swapping the batteries and not rewiring anything).

Hope this helps.
 
I'll keep the wring options under consideration, but I'm onto the DC-DC charger configuration and my alternator woes.

Here are the 4 prescribed ways of configuring batteries in parallel as shown on the Victron website.

Screenshot 2024-04-24 at 10.46.20 AM.png

I have essentially used the a combination of the first and second method, which corresponds to the installation manual.
 
Last edited:
Sorry if we drug this out. We just don't want to see your batteries die needlessly at an inopportune moment.
 
All set . . . I re-wired things over the past few days according to my design changes and installed the panel in my boat this morning.
.
IMG_6160.JPG
.
I decided to activate the DC-DC charger with a combination of signal from the ignition key switch and engine running detection. It seems to work well. I made a section of the Delphi Metri-Pack cabling with a tap into the ignition wire. This way I did not have to cut into the OEM harness.
.
IMG_6151.JPG
.
Once the engine was running the charger went into bulk charging mode and then after a while went into absorption mode.
.
The BlueTooth feature of the Orion Charger is pretty cool. . . . I wish the EPEver had the same.

Here is the Orion status screen while the engine was running. . . .
.
IMG_6159.PNG
.
I do want to monitor the starter battery voltage for a while . . . It seems that the Orion has a current draw even when not active. Just want to make sure it is not excessive vs. what the solar charger can keep up with.
 
Last edited:
Sorry I'm late noticing this thread. I would think you need regulators on your alternators to manage the charge profile for either your lead acid batteries or (especially) for the LiFePO4 batteries. The Balmar regulator is the simplest (but is a pain). The Wakespeed-500 is much better, but still a pain. I've seen videos on YouTube about the new Arco Zeus regulator, and it sounds fantastic.

Sounds like the OP has already moved away from directly charging the LiFePO4 from the alternator, but one of the risks of doing so (that I think was mentioned by someone else) is that if the BMS disconnects the battery the Alternators will be spinning with no load and the windings will quickly burn out. Any of these regulators will manage that situation as well.
 
Last edited:
The DC-DC charger (Orion) is connected to the port side starter battery. The alternator charges the starter battery. If/when the BMS disconnects the starter battery absorbs any voltage spike. This is a fairly common design practice.

My previous approach, as mentioned, was to go to the DC-DC charger directly from the alternator . . . that approach did not work out.. It really needed a smart alternator (or at least the Balmar) to do that. It was never set up to charge the LFP batteries directly from the alternator . . . the DC-DC charger was always in the mix.

I also sized the DC-DC charger at less than half the alternator rating (30 amp Charger, 70 amp alternator) to go easy on the alternators.
 
Last edited: