150A main breaker is for up to 120A continuous current (either loads or backfeed, but don't worry about sum of those two.)
200A main panel busbar x 120% = 240A
240A - 150A main breaker = 90A backfed breaker allowed.
(Or did you say a 225A busbar was put in it? Would be nice to have a sticker saying so if that's the case.)