Cell health in a 16s pack

Wildly out of balance.
+1 this has to be the craziest cell graph that I have come across...

I would not balance via the BMS but take the pack apart and put all the cells in parallel and charge them up to 3.55.
When you do this make sure the pos. and neg. leg of the charger are on the opposite ends of the pack to ensure the charge 'flows' through the pack effectively. Depending on the charger size it may take a while but make sure you do not over charge the pack.

I believe Will has a good video recapping the process I mentioned above.

Once all the cells are balanced then put them together and make sure the torque settings are similar to avoid a loose connection. From there you should have a good baseline to determine if you have some laggard cells.
 
+1 this has to be the craziest cell graph that I have come across...

I would not balance via the BMS but take the pack apart and put all the cells in parallel and charge them up to 3.55.
When you do this make sure the pos. and neg. leg of the charger are on the opposite ends of the pack to ensure the charge 'flows' through the pack effectively. Depending on the charger size it may take a while but make sure you do not over charge the pack.

I believe Will has a good video recapping the process I mentioned above.

Once all the cells are balanced then put them together and make sure the torque settings are similar to avoid a loose connection. From there you should have a good baseline to determine if you have some laggard cells.

Here is the today chart before I took the pack apart to top balance again in //, did as last time opposite pos. and neg. actually saying ~4A, and 3.421v at the legs.
1646940987580.png
 
It's almost like the cell balancing process that the BMS may be attempting is corrupted. It tries to balance but pushes more volts than it should. Like it's pulling volts out of all the cells but two and sending that voltage to the two cells.
 
Simple answer, #13 is always lowest v on discharge and always first to reach cutoff when charging… the cell is lowest capacity.
to @Alexplose I'm going to say (having read the whole thing at least passingly) what I think you need to do is individually charge each cell and monitor current and take each cell to the 3.65V level and measure the input current (I use a tool like a 150A in line which reports to me the voltage and the amps and other details in summary). Do this for each cell. Then do a discharge test at something like C or half C and again document that. This will (imo)
  1. clarify cell capacity
  2. provide useful data for a claim from the seller
sadly all cells are not created equally, and those which are cheaper are typically not tested before sale. Meaning you need to do the testing and QA.

Just my view.

NOTE: this is my 150A
1646948078290.png

Lacking a good measurement system I just put my GoPro on a gorilla pod and set it to take a still every 5 minutes ... then I just go through from the last image and can plot data from that ... of course the summary of Wh and Ah in (and of course turn it around and "out") is immediately helpful without referring to the "history data".

also, if not using a BMS make sure you don't go into over discharge or over charge!

Best Wishes
 
It's almost like the cell balancing process that the BMS may be attempting is corrupted. It tries to balance but pushes more volts than it should. Like it's pulling volts out of all the cells but two and sending that voltage to the two cells.
this is a good theory and different BMS's have different capacity for a delta V between cells (especially passive type BMS).
 
so, which cell(s) are this/these
View attachment 86822


one looks to be 11 the other maybe 12

Have you tried turning off the balance function or at least raise the trigger voltage to 3.55 or 3.6? It would be interesting to see if that is causing the issue (BMS). Having that many cells go haywire like that makes me think this is not a single or two cell issue but a BMS issue.

FYI -
Here is my graph for a 16 280ah cells. Notice at the low range (AM) the cells have a delta of .05 or so (bottom of the cell knees) I do not balance since this is 'normal' for my cells, once they start to charge they have a delta of 0 or .01, again no balance function is enabled. They will stay this way until the upper knee but by then I have a shut off charge on the mppt to stop charging the battery, I stick to a 20-80% capacity range for longevity. The green line is the overall pack voltage.

Screen Shot 2022-03-10 at 7.05.30 PM.png
 
If you "top balanced" your cells to 3.55 you didn't top balance you cells. Fully Top balance to 3.65 you won't hurt the cells if you're doing this properly.

The very first time you got your cells and you said you top balanced the was is 3.65 or 3.55?
 
If you "top balanced" your cells to 3.55 you didn't top balance you cells. Fully Top balance to 3.65 you won't hurt the cells if you're doing this properly.

The very first time you got your cells and you said you top balanced the was is 3.65 or 3.55?
@Alexplose Just be very careful going the last .1 volts. there is very little AH left and you'll reach 3.65 a lot faster than you expect... I know i overcharged a few cells when i first put my pack together.
 
Is this top balanced when the voltage accross the pack is 3.654V, and the individual cells are about 3.650-1V, charger is still pushing some amps, I disconnected, will let rest and see the resting voltage.
 
Is this top balanced when the voltage accross the pack is 3.654V, and the individual cells are about 3.650-1V, charger is still pushing some amps, I disconnected, will let rest and see the resting voltage.

"I disconnected" - assuming you mean disconnected from the charger.

Once you terminate charging, you need to disconnect them from being in parallel. If you leave them in parallel, they will all stay at the same voltage. Disconnecting them will allow you to see any outlier behavior.
 
"I disconnected" - assuming you mean disconnected from the charger.

Once you terminate charging, you need to disconnect them from being in parallel. If you leave them in parallel, they will all stay at the same voltage. Disconnecting them will allow you to see any outlier behavior.
Yes that's it, so now I need to take them apart and see which one is mis behaving.

I measured 3.642, 3.643 on all cells how many time before I can see something ?
 
Last edited:
Yes that's it, so now I need to take them apart and see which one is mis behaving.

I measured 3.642, 3.643 on all cells how many time before I can see something ?
+1 day but i am not sold it is a cell that is the problem from reviewing your graphs & given a large number of cells are showing wide swings. my bet is a bad bms or bad bms setting or wire / connection issue.
 