Just replaced our Daly 200a BMS with a JBD 200a. The Daly had 2 gauge silicone pigtail cables preinstalled on the B- and P- terminals. Used 10-12" long 2/0 cables with the JBD. Almost .1v less voltage drop with a 150a load with the 2/0 (vs. 2 gauge).
Also replaced a generic, plastic 200a ANL fuse with a Bussmann Eaton 200a ANL fuse. With 120a of current, experienced a 55mv drop with the generic fuse. Only a 42mv drop with the Bussmann Eaton fuse.
It all adds up.