onpointe33
New Member
Hi! New to the forum here though been reading since last year.
Currently have the Ecoflow Delta Pro 3.6kw connected to six 100W panels and two 200W panels in parallel (3 100w and a 200w connected with a BougeRV 4 to1 on either side, connecting both to a Y connector going to extension cable).
Max charging in full FL sun is only coming in at 300W and was scratching my head. I'm realizing that current is way over maximum at 70A (1600W Max, 11-150V, 15A Max) for Delta Pro.
I'm considering parallel/series combo however the fact that I've got the (2) 200 watt panels in the mix I would really appreciate some suggestions for an optimal setup as I understand that it shouldn't be in series with the 100Ws.
Should I just replace the 200w panels with 100w panels and run a 4s2p? Could I still run a 4s2p with one of each branches having (3)100w and (1)200w?
Is there an entirely different setup that would be better that my novice brain hasn't thought of?
Thanks!
Currently have the Ecoflow Delta Pro 3.6kw connected to six 100W panels and two 200W panels in parallel (3 100w and a 200w connected with a BougeRV 4 to1 on either side, connecting both to a Y connector going to extension cable).
Max charging in full FL sun is only coming in at 300W and was scratching my head. I'm realizing that current is way over maximum at 70A (1600W Max, 11-150V, 15A Max) for Delta Pro.
I'm considering parallel/series combo however the fact that I've got the (2) 200 watt panels in the mix I would really appreciate some suggestions for an optimal setup as I understand that it shouldn't be in series with the 100Ws.
Should I just replace the 200w panels with 100w panels and run a 4s2p? Could I still run a 4s2p with one of each branches having (3)100w and (1)200w?
Is there an entirely different setup that would be better that my novice brain hasn't thought of?
Thanks!