How hot is to hot? Combiner box

Any significant heat spot is a point needing attention.
The fact it is 130 on that screw, but nowhere else on the circuit says to me the device has a bad connection, not a bad wire
 
It was still over 90F after sitting for over 5 minutes.
Direct to the breaker now, 40A Chitaxi.
img_thermal_1708877710231.jpg
 

Attachments

  • img_thermal_1708877710231.jpg
    img_thermal_1708877710231.jpg
    91.3 KB · Views: 6
  • img_thermal_1708877666169.jpg
    img_thermal_1708877666169.jpg
    82.3 KB · Views: 8
  • IMG_20240225_111032.jpg
    IMG_20240225_111032.jpg
    69.7 KB · Views: 7
  • IMG_20240225_111006.jpg
    IMG_20240225_111006.jpg
    53.4 KB · Views: 7
  • IMG_20240225_110936.jpg
    IMG_20240225_110936.jpg
    56.8 KB · Views: 8
  • IMG_20240225_110919.jpg
    IMG_20240225_110919.jpg
    54.7 KB · Views: 7
Copper conductors both heat and electricity, so a bad connection or bad fuse holder will cause the wire to get hot.

Did you try loosening and retorquing the clamp screw? If so, I'd pop open the fuse holder to see what's inside.
 
One thing to note is I did split the holder apart, it was 3p. That shouldn't have had any impact at all since it was just a pin holding them together, nothing to do with the wire connection.
 
Copper conductors both heat and electricity, so a bad connection or bad fuse holder will cause the wire to get hot.

Did you try loosening and retorquing the clamp screw? If so, I'd pop open the fuse holder to see what's inside.
Yes, no difference before and after replacing the wire as well.

I was having issues blowing 20A fuses a few days / weeks back but figured that was because I was running ~22A through them. I used a 25A I ordered the other day and figured I'd check temps after the recent fire thread...
Everything with the holder appeared fine.

I'll get some Midnite holders on order and see if they make a difference.
 
Why are the spec on the front (32a @ 690vac) vs the side (30a @ 750vac)?

Is that fuse holder rated for DC? It probably doesn't matter it's just a fuse holder, the fuse is the important part.

Pics of the inside?

What current was the constant current running through it and the fuse rating?
 
Yes, no difference before and after replacing the wire as well.

I was having issues blowing 20A fuses a few days / weeks back but figured that was because I was running ~22A through them. I used a 25A I ordered the other day and figured I'd check temps after the recent fire thread...
Everything with the holder appeared fine.

I'll get some Midnite holders on order and see if they make a difference.
I see you posted the answer to my current question just as I was asking it.

22 amps continuous throughout a 25 amp fuse, is likely the problem. A fuse is a resistor and creates heat to melt and blow.

Normal recommendation is to run a fuse at a max of 80% continuous. Stepping up the fuse to 30 amp would be the minimum to meet that spec.

Was the other holder doing the same current?
 
I had a similar issue at the breaker.
Was getting hot enough to trip it .
I THOUGHT I was able to 'torque' the screw down with just a screwdriver in my hand but went ahead and put a bit holder and bit on my torque wrench.
More than half a turn later, the issue iwas fixed.
 
I also removed the big diodes with heat sinks in my combiner because they produce a lot of heat in a sealed box.
Swapped in a bus bar.
 
Why are the spec on the front (32a @ 690vac) vs the side (30a @ 750vac)?
That's a good question.
Is that fuse holder rated for DC? It probably doesn't matter it's just a fuse holder, the fuse is the important part.
According to the Amazon listing, yes.
Pics of the inside?
Can't get much without breaking it open.
What current was the constant current running through it and the fuse rating?
I see you found it.

I see you posted the answer to my current question just as I was asking it.

22 amps continuous throughout a 25 amp fuse, is likely the problem. A fuse is a resistor and creates heat to melt and blow.

Normal recommendation is to run a fuse at a max of 80% continuous. Stepping up the fuse to 30 amp would be the minimum to meet that spec.

Was the other holder doing the same current?

No. The other strings (roofs) are running around 340V 9A at peak conditions but are combined after the fuse.
The ground mount fuse in question is paralleled at the array.
 

Attachments

  • IMG20240225112814.jpg
    IMG20240225112814.jpg
    83.5 KB · Views: 3
  • IMG20240225112919.jpg
    IMG20240225112919.jpg
    71.1 KB · Views: 3
  • IMG20240225113009.jpg
    IMG20240225113009.jpg
    62.8 KB · Views: 3
  • IMG20240225113041.jpg
    IMG20240225113041.jpg
    134 KB · Views: 3
  • IMG20240225113103.jpg
    IMG20240225113103.jpg
    70.9 KB · Views: 3
I had a similar issue at the breaker.
Was getting hot enough to trip it .
I THOUGHT I was able to 'torque' the screw down with just a screwdriver in my hand but went ahead and put a bit holder and bit on my torque wrench.
More than half a turn later, the issue iwas fixed.
I'm confident they are tight enough.
If I go any tighter I'll break something.
I could see the plastic flexing when tightening...
I was able to get another ¹/⁵ a turn on the other connections that aren't getting hot.
 