Lead acid battery capacity is specified at certain discharge rates . Your battery specification should tell you if the rate is, 100 hours, 20 hours or 10 hours. My guess is your 170 Ah is at the 100 or 20 hour rate and the capacity at the 10 hour rate will be nearer 150 Ah.
From what I found on Enersys site, it is a telco application.Max charge rate , cyclic use, from data sheet 0.5 C, 85 amps. Seems a bit high to me for an AGM battery, I would expect 0.2C to 0.3C.
Is the battery new or SH from a telecommunications application?
I'm editing here to prevent some confusion. I did look at the manual on Enersys and it did not have graphs. I did run across this manual, https://manuals.plus/enersys/v-ft-powersafe-battery-manual#axzz83697prdOMike has it correct. The small 10 is denoting it is a 10 hour rated battery, in other words, at the 10 hour charge and discharge rate, the battery capacity is 170Ah.
Take the 170 divided by 10= 17A
17A x 0.5C= 8.5A charge rate typically used as a maximum
The battery can be charged at a higher rate, but that may affect battery longevity.
Is the battery new or SH from a telecommunications application?
If I was charging this battery, I would use 0.3C rate as any maximum.
One should know what the max charge rate should be so it is never exceeded.I have never understood why people wish to know what the absolute maximum of anything is, right up to the point of permanent damage or destruction, then decide to routinely run it at that level.
Yes quite so.
I agree, I de rate items all the time.But many people do not seem to understand that de rating equipment is usually very necessary for long term reliability.
Yes quite so.
But many people do not seem to understand that de rating equipment is usually very necessary for long term reliability.
Haha, very true !BUT! It's very hard to derate when you don't know the rate in the first place