Do the lights on the Watt Node show importing or exporting? I think green lights are power in and red is power out, or do I have that backwards? The manual I found says Green flashing for positive power and red flashing for negative power. Installed by their instructions, red is power going to the grid. Maybe you need to turn around the CTs or their wires to make it go the right way?
It would not shock me if Schneider got the data flipped, but flipping the CTs should still fix it to show right in the software. Looking at mine right now, the grid power shows a positive 322 watts when it is exporting to the grid. A Negative power in the Schneider world would be pulling power from the grid. That is backwards from what the Watt-Node manual shows.
It would not shock me if Schneider got the data flipped, but flipping the CTs should still fix it to show right in the software. Looking at mine right now, the grid power shows a positive 322 watts when it is exporting to the grid. A Negative power in the Schneider world would be pulling power from the grid. That is backwards from what the Watt-Node manual shows.