I assume you are connecting SA to the RS485 port just below the CAN port (which is above the positive connection) used to connect to the inverter.
The manual states that pins 1&2 as well as pins 7&8 are the RS485 bus pins. Which two pins is the cable to SA using? SA sends command data to each battery and it is possible the master battery is interpreting these SA commands as coming from the inverter and instructing a shutdown. I don't know what communication protocol (e.g. Pylontech, PACE, EG4, Narada etc) is used on the RS485/CAN port and this can be an issue if you do not have the correct protocol selected in SA.
Some EG4-LL have the CAN/RS485 and the battery to battery ports located different that I described above but the general ides is the same.
The two ports below the Positive connection are I assume to daisy chain the batteries together. The manual indicates pins 1&2 as well as pins 7&8 are used for RS485 buses. For EG4 LifePower4 batteries, pins 1&2 are one bus and pins 7&8 are another. Again, For EG4 LifePower4 batteries the master battery communicates to the others using pins 7&8 which allows SA to use pins 1&2 to poll all the batteries. Don't know if the EG4-LL batteries are the same or if they use both pins 1&2 and 7&8 (like Sungoldpower batteries). You could try connecting SA to the open port on the last battery using pins 7&8 on that port. I am not sure what protocol to select on the SA configuration tab but for the EG4 LifePower4 batteries I use "Narada" as that is the protocol used in these batteries. It is possible the EG4-LL use the same protocol.
The EG4-LL manual I looked at also shows on page 14 that there is an EG4 LifePower4 battery at the bottom of the stack so it is a good possiblity that pins 1&2 on the last battery (battery to battery ports) will work for SA.
Give it a try.
The manual states that pins 1&2 as well as pins 7&8 are the RS485 bus pins. Which two pins is the cable to SA using? SA sends command data to each battery and it is possible the master battery is interpreting these SA commands as coming from the inverter and instructing a shutdown. I don't know what communication protocol (e.g. Pylontech, PACE, EG4, Narada etc) is used on the RS485/CAN port and this can be an issue if you do not have the correct protocol selected in SA.
Some EG4-LL have the CAN/RS485 and the battery to battery ports located different that I described above but the general ides is the same.
The two ports below the Positive connection are I assume to daisy chain the batteries together. The manual indicates pins 1&2 as well as pins 7&8 are used for RS485 buses. For EG4 LifePower4 batteries, pins 1&2 are one bus and pins 7&8 are another. Again, For EG4 LifePower4 batteries the master battery communicates to the others using pins 7&8 which allows SA to use pins 1&2 to poll all the batteries. Don't know if the EG4-LL batteries are the same or if they use both pins 1&2 and 7&8 (like Sungoldpower batteries). You could try connecting SA to the open port on the last battery using pins 7&8 on that port. I am not sure what protocol to select on the SA configuration tab but for the EG4 LifePower4 batteries I use "Narada" as that is the protocol used in these batteries. It is possible the EG4-LL use the same protocol.
The EG4-LL manual I looked at also shows on page 14 that there is an EG4 LifePower4 battery at the bottom of the stack so it is a good possiblity that pins 1&2 on the last battery (battery to battery ports) will work for SA.
Give it a try.