Each source OCPD must be 13.93 x 1.56 = 21.73, round it up to 25A
Source cable must be rated for more than OCPD - AWG10 (30A)
AWG6 from combiner to SMBS
Am I on the right track here?
Thanks
I bought it years ago for a project that had to be abandoned shortly after. Figured I might as well use it since I already have it. Battery is 24v (8 230Ah EVE cells). What I'm trying to do is power my recreational getaway during the warm and sunny months.
Thanks.
Hey, everyone.
I'm thinking of getting three of these panels to be hooked up to Electrodacus SBMS40:
Canadian Solar HiKu6 Mono PERC
CS6R 405MS
Nominal Max. Power (Pmax) W 405
Opt. Operating Voltage (Vmp) 31.0 V
Opt. Operating Current (Imp) 13.07 A
Open Circuit Voltage (Voc) 37.0 V
Short...
Yes, I was looking at those, but are they safe to use in my situation even if I up the fuses to 25A? Let's take Vevor box for example; does it look like it can handle potential 42A? They all seem to be rated 10-15A regardless of the size of the fuse.
Vevor box: https://tinyurl.com/vf2kh6re
Thanks!