Thanks for all the advice. After continued testing, it appears that the generator voltage is also causing some problem. I connected my true grid power, then disconnected the solar, turned the breaker off from the batteries, and the ac voltage from the grid is coming and supplying the coach. When...
Well I worked out a solution and have installed it. First off I unhooked the genny wiring from the transfer box at the rear of coach where grid versus genny determined. I located the genny wiring that was going down the middle of coach and cut the cable so that it no longer went to the back...
Found a video where guy that was testing different scenarios and his conclusion was the same on the 240vAC . He could not find anyway to get it run on 120vAC even though specs state "AC Input Data-Nominal AC voltage=120-240vAC. Trying to determine best path forward as the rest of my rig runs...
Thanks for your reply. The AIO has the ability to use either SOC or time settings, which in the bigger picture makes since so everything can run automatically. But from what I can tell, the battery has to be discharged to less than 90% before it allows charge from the grid. Others have made a a...
I have found more clues to my generator issue. When I measure grid L1 & L2 at the transfer switch, I get 120v on each and when I measure L1 & L2 together I get 240v. When I measure the generator L1 & L2 at the transfer switch, I get 120v each but when I measure L1 & L2 I get 0v. Since it's not...
I have an EG4 6000XP in my rv running off solar, battery, grid/generator. When I say grid/generator I mean I left the original transfer switch in place so when the ac is sent to 6000 xp it could be from the actual grid or my onan 7500qd. Each are identical in that they are 2 legs 120v. I have...