It's a hanging curve ball and I appreciate your willingness to put some thought to it. I have made 3 attempts to contact the vendor but seem to be left to my own devices. To level set my issue, the fault was intermittent prior to my system being torture tested by the week long polar vortex. I...
I am no SME in this field but the installation manual states not to for parallel spit phase when installing "Two inverters parallel, 1 + 1 system". 1 inverter per line feed. If I was needing to draw more current than a single inverter can put out, I can add 1 more inverter to that leg, that is...
This is all that is referenced in the manual
5. Wiring of Current Sharing Cable
Parallel connection in single phase: Current sharing cable line is the twisted
connection cable. Ensure the “one-in-one out” rule when connecting each
inverter, connect the current sharing cable of the inverter with...
Good Morning,
I am using 2 Solar Hybrid Inverter/chargers, with Grid bypass in a parallel 240V spilt phase configuration. It is a small system intended primarily for my 240 slow start well pump and 2 deep freezers. My PV is wired to only one inverter for my 6-345W Mission Solar panels wired in...