Thank you for the charts. Good to see your bus voltage is similar to mine. Also the parameters are quite the same, the 57 was 1[A] and most probably that alone led to battery over volt. As for main bus over volt, I won’t fiddle with grid on for now because the inverter works fine otherwise...
I have a 10kW Easun split phase that can back feed the extra solar to grid. I need help understanding the back feed, since the inverter has both ac input and output ports.
Question is: does it back feed directly via the ac input port? If the grid fails does it know to isolate the input in order...
1. I don’t have any agreement. I don’t run in grid tie mode. Just happen to try it briefly once. I have two uncomissioned inverters with export limiters to address the consumption on the extra panel connected to grid only. The solar setup-excepting for the grid tie inverters feeds a panel that...
the solar array doesn’t get above 400v usually but the inverter dc bus gets above 520, as seen on attached charts. I have to say that while the bus voltage fluctuates the ac output is consistently solid; there is no indication in the output that the dc bus misbehaved. However, looking at the...