Doesn’t that seem really unlikely? Occam‘s Razor says it was some kind of frequency measurement error, maybe caused by powerline interference?
It’s always string A.
I have one pv array but paralleled it with MPpT B so technically both MPPTs are running together on the same feed
Frequency monitoring upper maximum threshold 62.00 Hz, think this is disconnect for 5 minutes
Frequency monitoring, lower maximum threshold 60.50 Hz, think this is start of Rule-21 frequecy-watts
Island Mode Start. point of the power control via frequency 1.00 Hz, 60 + 1 = 61 Hz, only applies to completely off-grid system (well, SMA America said to use Island mode on grid behind Sunny Island, but I have concerns about that.)
I'm surprised it is every anything other than 60.0 Hz. Assuming you're on grid, not behind Sunny Island.
You and I are on the same western half of US.
60.4 Hz isn't supposed to curtail, but you may have misted 60.5 or higher.
"Manual setting active power limitation P, active power configuration - 3890W" I guess that's your 3.8kW inverter.
For my SBS, I think I've seen option of either % of available PV power, or % of max rated power. I don't see that in yours.
It seems like the entire Western half of united states had elevated frequency to curtail production, and you experienced it.
You have the ability (but I suppose not the legal authority) to adjust frequency where curtailment occurs.
Perhaps this is only occasional and you can live with it, do your part to avoid destabilizing the grid.
As an experiment you could disable, see if system is capable of delivering full power, either by changing frequency limits or by using UL-1741 not Rule 21.
If derated for temperature (not what OP's inverter messages indicate), look into Vmp and inverter efficiency tables.
The difference between 98% and 99% is 2x the power dissipation in inverter.
So maybe a different number of strings and length of strings would let inverter run cooler.
Also, utilizing more MPPT. Sometimes people put all PV as a single string on input A only. Splitting into two separate strings, or paralleling MPPT A & B (for inverters which allow that) should increase efficiency.
One string of 9 panels. See previous post for photos. Basically one string feeds bith mppt s.how much panels you have per string/mppt... could be also too much voltage per string.... check inverters capability per mppt
Two MPPTs are outputting values. Identical values. Picture.Now that seems odd. Can you see output or voltage and current of MPPT A and MPPT B independently?
(I'm wondering if the paralleling isn't actually done, like an open wire, so only string (MPPT) A is involved.
Is two short strings, one per MPPT, convenient to try? (but paralleling has worked for others who had clipping or some sort of derating.)
And of course, try diddling with parameters as a test.
Got a scope or digitizer to see what waveform is showing up as 60.4 Hz?
Actually grid tied inverters will put the maximum available power back into the grid that is available, unless they have been somehow commanded to produce less. DC coupled inverters are different.You ARE aware that a solar installation only delivers what your LOADS are right?
If it is specced to a certain wattage it does NOT deliver that at all times.
Also, clouds/unclear weather...
Airflow is not blocked. The inverter is installed exactly per manual. I will monitor the inverter radiator temperature for a couple of days i guess, just to confirm that going to use a smart temperature sensor.No need to split between MPPT now that you've confirmed power is divided 50/50.
And power level too low to derate for heat. Any chance airflow is entirely blocked?
The funny thing is elevated frequency. Some if your displays is was close enough to 60 Hz.
What fraction of time is this occurring, and what fraction of available power lost? If occasional maybe not a big deal.
Have to wonder if grid impedance and anti-islanding confuses frequency measurement. Maybe other loads, or a neighbor's PV.
You could try shutting off all breakers except the inverter, if you have any funny loads. Grasping at straws here, without anything to display voltage waveform.
60.4 Hz again! But a no-name voltmeter, with 1 significant digit after decimal place. I would trust Sunny Boy more.
Yabut IIRC 0.2 Hz something seriously wrong with the grid, like load or generation shedding before it all blows up, so it just feels really unlikely that the western US would be that far out and no-one noticed.Yes but ... Sunny Boy and DMM both saw elevated frequency. While RMS voltage might be a single correct value, what does "frequency" even mean when there are many frequencies present? Zero crossings? Highest peak of FFT?
(I ask this often using FFT to study noise issues, and it isn't the way to actually determine precise frequency.)
Yabut IIRC 0.2 Hz something seriously wrong with the grid, like load or generation shedding before it all blows up, so it just feels really unlikely that the western US would be that far out and no-one noticed.
I don't think there is any safety risk in turning active power limitation off. That just makes it behave like older versions of inverters, doesn't help maintain grid stability.
My DMM just said 60.02 Hz. Two counts in least significant digit might me measurement error, or real.
0.2 Hz delta would be a big amount.
If OP is only seeing 60.4 Hz on DMM, not on Sunny Boy, I would assume something else caused derating.
But wasn't the error message frequency related?
507 | Active power limit AC frequency |
8006 | String A is in derating mode |