[Resolved] System is down Sungoldpower 8K Hybrid inverter - Need urgent help

Is that even a term? If the circuit is OPEN, no current flows.

SHORT circuit amps, I have seen before. (Isc)
Exactly my point, mvreddy48 doesn't seem to understand the basic terminology or the use of his test equipment, which is a bit disconcerting when he's playing with high voltage DC strings. Hey, everyone has to learn sometime, but if you are getting the basics wrong (or backwards) that's the time to take a step back and understand the system.
 
Same results as above with MPPT2. Around 320V and 0 AMPs on inverter. But open circuit amps are around 40 amps.
Not the same. You other image showed a connection to the solar panels. This one shows voltage only but no line to the inverter. It also shows a full battery, not in Bypass and 1 amp load on the battery.

Something is going on with your setup but it is a bit hard to diagnose remotely. Perhaps simplify things by turning off utility and just run a load off the inverter for a while and see if as the battery drops in charge so that your solar begins to feed.
 
Can you post your settings?

Are you in SBU (or even SOL)
What voltage do you have for setting 4 and 5?
In setting 6 are you in SNU?
What amps do you have for setting 7?
What is setting 71 set to?
 
Your battery is showing as full so it won't take a charge.
To check the current you could use the clamp meter around the wire and short the solar panel + and - together; I would only do this with one panel.
I'm not familiar with that meter, does it have a zero function before checking current?

I really suspect it's a setting issue or poor connection.

How do your settings compare to these?
Post in thread '4 MWh SRNE ASF48100U200-H 10kw.' https://diysolarforum.com/threads/4-mwh-srne-asf48100u200-h-10kw.67809/post-1044376
Thank you, I will post it soon.
 
Can you post your settings?

Are you in SBU (or even SOL)
What voltage do you have for setting 4 and 5?
In setting 6 are you in SNU?
What amps do you have for setting 7?
What is setting 71 set to?
I will post it soon.
 
OP please be very careful as you are messing with 320 volts DC and that shit will hurt you bad. It is obvious you have limited electrical knowledge but you are learning and getting there so well done, just please be careful.
Thank you!
 
I initially thought the same, but SOC was 5% at the beginning of this thread.
I charged the batteries via Utility/Grid yesterday night to SOC 90% by changing the parameter 6 temporarily (to Utility can charge batteries if Solar power is not available) and it charged fine.
 
Your battery is showing as full so it won't take a charge.
To check the current you could use the clamp meter around the wire and short the solar panel + and - together; I would only do this with one panel.
I'm not familiar with that meter, does it have a zero function before checking current?

I really suspect it's a setting issue or poor connection.

How do your settings compare to these?
Post in thread '4 MWh SRNE ASF48100U200-H 10kw.' https://diysolarforum.com/threads/4-mwh-srne-asf48100u200-h-10kw.67809/post-1044376
Thank you, I will review this thread.
 
Utility/Grid yesterday night to SOC 90% by changing the parameter 6 temporarily

I think that was a good test to rule out any issue with the charging, connection to battery bank and battery bank itself.

This leaves only these options for the problem:

* AIO's MPPT (unlikely since both of them show the same failure to charge)

* wiring between panels and AIO.
Is it still configured as 2P4S? No combiner box, I assume. As was suggested before, maybe change the panel configuration to 1P4S .. less connections, to locate a bad connection.

* a problem in a solar panel???
 
Thank you, I will review this thread.
It's long and all over the place but I linked to the settings I've been using successfully for months now.
They are for open loop 16S LiFePo4 with grid usage as last priority.

I'm hoping you can figure out the root cause quickly.
 
I wonder if the open-loop thing is causing you problems. Is it possible the battery is out of balance or just needs its SOC meter reset?
 
I wonder if the open-loop thing is causing you problems.
Highly doubtful. I have over 6 MWh through 2 different inverters, never used battery--inverter comms.
Is it possible the battery is out of balance or just needs its SOC meter reset?
It's possible but his display should show if it were charging with solar.
Attached mine for reference.

Edit - proper units.
 

Attachments

  • IMG_20240421_134637__01.jpg
    IMG_20240421_134637__01.jpg
    142.3 KB · Views: 2
  • IMG_20240421_134857__01.jpg
    IMG_20240421_134857__01.jpg
    45 KB · Views: 2
  • IMG_20240421_134638__01.jpg
    IMG_20240421_134638__01.jpg
    225.6 KB · Views: 1
  • IMG_20240421_134647__01.jpg
    IMG_20240421_134647__01.jpg
    123.4 KB · Views: 1
  • IMG_20240421_134648__01.jpg
    IMG_20240421_134648__01.jpg
    96.3 KB · Views: 1
  • IMG_20240421_134907__01.jpg
    IMG_20240421_134907__01.jpg
    93.1 KB · Views: 2
Last edited:
Can you post your settings?

Are you in SBU (or even SOL)
What voltage do you have for setting 4 and 5?
In setting 6 are you in SNU?
What amps do you have for setting 7?
What is setting 71 set to?
01 is UTI currently, usually it is on SOL but the moment it is put on SOL it starts pulling the Amps from battery (which I charged last night through Grid).

For 4 and 5 the voltages are default 43.6V and 56.8V.

7 is 60 amps.

I don’t have setting 71. The parameters are until 68 only for this inverter.
 
Have you tried 01 in SBU?
What is setting 06 currently?
Have you tried a complete power down and restart?

Nothing was changed before it stopped charging from solar?
 