diy solar

diy solar

4 T-105 batteries 6v each wired to 12v

nschizzano

New Member
Joined
Apr 16, 2024
Messages
24
Location
Ottertail
So 4 T-105 batteries, each 6 volts and 225 amp hours. Wired to achieve 12 volts has a total amp hourage of 900ah?

Thanks yall
 
Nope.

I am going to assume you are referring to a Trojan T-105 golf cart battery, not the RE or solar versions which are taller with more electrolyte.

In any event, they are rated for a C20 of about 225 amps at 6 volts. If you put 2 in series, you will have 12 volts with a C20 of 225 amps. If you then take the 2 in series and connect them in parallel, you will have 12 volts and a C20 of 450 amps.

Just in case, a C20 is the manufacturer rating for amperage (power) if you draw down the battery over 20 hours. Pretty standard for flooded lead acid batteries.

On the other hand, the lithium iron phosphate batteries are often quoted with a C1 or C2, for both charging and discharging over 1 or 2 hours.
 