Do I need diodes in this battery design?

moonlight23

New Member
Joined
Aug 8, 2022
Messages
47
I’m building a portable battery power station and I want to use a MPPT charge controller to charge the battery from solar AND AC power from the wall. Both will be connected to the PV input on the MPPT.

Will there be issues with current backflow from solar panels to the PSU, or from the PSU to panels? If so, would some diodes (yellow boxes) prevent this? What diode value would I need?

PSU is a Meanwell LOP-600-36 (16A, 36v) and the MPPT is a Victron 100/15 (15A, 100V).

Screenshot 2024-05-02 at 3.03.03 PM.png
 
I do not understand, why wouldn't you just connect a regular charger to the battery?

This seems to me like making poor compromises for no reason or because you already have part of the equipment like PSU?
 
Why not just use a 24V charger like NPB-360-24
I do not understand, why wouldn't you just connect a regular charger to the battery?

This seems to me like making poor compromises for no reason or because you already have part of the equipment like PSU?

I want this all contained in a case where I just plug in a cable into the case, that's connected to the PSU input. Dedicated chargers are too large to shove in the case, even the Meanwell NPB-360-24.

I'd later also have the PSU 36v output connected to outer terminals if I never need 36v DC for whatever reason.
 
or a LOP-600-27

That has adjustable voltage of 25.6-28.4V

How would this 27v PSU work for this situation? Wouldn't it not float-charge once the batter is almost full? I don't want to manually monitor the charging and disconnect when required. I'd rather just let the MPPT not pull anymore power when the batter is full. Let me know if I'm missing something.
 
You would need a blocking diode rated for Isc on the solar panels. You might or might not need a blocking diode for the power supply, I’d put one in anyway.

 
^ Thank you, that's very helpful!

And just to clarify, I would never be charging the battery from solar panel and wall AC at the same time. I suppose that would make it pointless to put blocking diodes on the panels? I'll add one between the PSU to the MPPT though.
 
You watched the video, yes? You want to prevent the panels from acting like giant (IR) LEDs when the power supply applies a voltage.
 
How would this 27v PSU work for this situation? Wouldn't it not float-charge once the batter is almost full? I don't want to manually monitor the charging and disconnect when required. I'd rather just let the MPPT not pull anymore power when the batter is full. Let me know if I'm missing something.

If this is LFP, you could simply set it for 27.2V and it would fully charge it. that's not an ideal float voltage, but it works.
 
MPPT charge controller to charge the battery from solar AND AC power
Use a battery charger connected to the battery.

The Meanwell type of power supply do not have an ideal current limit, they fold back or burn out if overloaded.

Connecting to the MPPT input via a diode, (only needed in the positive path of each source), may work, ( use a 35A bridge rectifier on heat sink, inputs to each ac tab, output from + tab).

A better , more eficient, safer, and correct charging, is a charger to the battery,
 
Other threads discuss using mppt to raise or lower voltage from a fixed source (battery or powersupply) to charge a battery. In short, the way an mppt works does not play well with the non-solar panel source.

Since the psu has more power than the mppt can use, it might work OK. I would put a switch to select one input or the other.
 
Last edited:
That sounds like a fun project! Every remote control on the block would stop working maybe? :)
You might have to modulate it (there’s a static IR source that probably swamps everything else) but it might be worth a try. If you know what brand of TV your neighbor has, you could probably modulate it with a volume up signal or something silly.😁
 
Last edited:
You risk frying the MPPT.

That meanwell can provide up to 25A (peak), thus exceeding the max input current of the MPPT of 15A.

Also, if you connect both panels AND the Meanwell in parallel, it will even easier exceed that 15A. Apart from that, not sure if the Meanwell does handle backfeeding (by the solar panels).
Would add one in the Meanwell just to be safe, but that does require a decent sized one (and probably require cooling)
 
You don't state what panels you have. Normally the power supply wouldn't care. Three 12V panels in series could exceed the output capacitor voltage specification as well as the diode.
 
Speaking of which, a neighbor is looking for a blocking diode, as his SCC appears to be discharging his battery overnight, what's a good source for those?
 
Why wouldn't you just feed a mean well straight into the battery? Are you trying to get the solar voltage to preempt AC supply voltage to effect a sort of SUB mode?
 
You risk frying the MPPT.

Not really.

That meanwell can provide up to 25A (peak), thus exceeding the max input current of the MPPT of 15A.

Power supplies don't force current. That's a surge rating should a load pull more than rated. For this PS to output 25A, that means the MPPT would have to draw WAY more that it's rated for on the output, OR polarity would have to be reversed.

The PV current input limit on Victron MPPT is for reverse polarity protection. The contactor that shorts the PV input if reverse polarity is detected can handle 15A without damage. If you do not reverse the polarity, there is no limit.

Also, if you connect both panels AND the Meanwell in parallel, it will even easier exceed that 15A.

Still not a concern unless polarity is reversed.

Apart from that, not sure if the Meanwell does handle backfeeding (by the solar panels).

In the dozens of MW supplies I've touched, they do have some sort of internal diode protection, but at what voltage does that break down?

Would add one in the Meanwell just to be safe, but that does require a decent sized one (and probably require cooling)

Without one on the panel, the PV panel offers a short circuit path while AC charging.
 
In the dozens of MW supplies I've touched, they do have some sort of internal diode protection, but at what voltage does that break down?
Mean well datasheets include an OVP range, but I'm not sure if that's just the range that they shut down into OVP or if it's their max rating of OV they can withstand.

I think it's the former, but in direct to battery applications I've never had to hit the range at all.
 