I have a JBD 100A BMS with two 10awg size wire per terminal. I feel like JBD knows what they're doing, but two 10awg feels undersized. I don't feel comfortable potentially running 100A through these stock wires.

Should I leave it or try to replace the wires with two 8awg wires?
 
I had similar thoughts about my JBD wires last year - see my thread here and the responses

 
There's almost no current going through those wires , other than passive balancing.
They are mainly used for voltage sensing I would expect
 
There's almost no current going through those wires , other than passive balancing.
They are mainly used for voltage sensing I would expect
It's the main wires, on the C- and B- terminals, not the tiny balancing/sensing wires.

10awg for balancing wires would be completely unnecessary lol
 
I had similar thoughts about my JBD wires last year - see my thread here and the responses

They are silicone 8 ga wires, ultra fine strand.

Your guys' 100A BMS looks like two 8awg wires, which would be fine and what I want to replace it with. The ones on mine is only 10awg, not 8awg.
 
Just for clarity:
20240509_175751.jpg

It looks like the insulation is indeed silicone rated for 200C which is good. But I thought temperature protection is separate than the actual current carry capacity, which is what affects resistant and voltage drop, and this depends on the cross section size of the conductor.
 
Just for clarity:
View attachment 214342

It looks like the insulation is indeed silicone rated for 200C which is good. But I thought temperature protection is separate than the actual current carry capacity, which is what affects resistant and voltage drop, and this depends on the cross section size of the conductor.


The copper in wire can carry absurd amounts of current. It's the temperature rating of the insulation that limits current. Your insulation can't catch fire.

One 10awg fine strand 200°C wire is good for 70A.
 
The copper in wire can carry absurd amounts of current. It's the temperature rating of the insulation that limits current. Your insulation can't catch fire.

One 10awg fine strand 200°C wire is good for 70A.

Thank you for the reassurance. 2x 10awg is equivalent to a single 7awg wire and no chart or forum posts I've seen says 7awg is fine for 100A (this forum tends to preach on oversizing on conductors).
 
Last edited:
If you look up awg tables, you're going to get the 60, 75 and 90°C ratings for enclosed wire in 30°C ambient.

Depending on the reference, 10awg wire won't fuse until > 300A for several seconds. The limit is the insulation and the conditions.

"battery" wire or "welding" wire has notably higher ampacity than what's in the awg chart.