I understand used solar panels produce less power. What I don't understand is... less what? Volts? Amps? Both?
Thanks for your help!
That would not measure real MPP output.1) measure voltage with voltmeter and then 2) short them and measure amps with clamp meter and then 3) volts * amps = watts to confirm output.
Not sure what this has to do with the question about how well used panels work.That would not measure real MPP output.
It's true, but your power output formula is ridiculously wrong.MPP has nothing to do with the panel itself.
Not 'ridiculously' wrong at all, but a simple a way to confirm the panel is working. Open circuit vs load is only a few volts - say 10v * 8a = 80w. The method will expose bad diodes as well. Even better is to get a known good panel and do the same test on both and compare the used against the known good one.It's true, but your power output formula is ridiculously wrong.
Open circuit voltage x short circuit current..? Try to measure them contemporarily!
Your formula is greatly over estimating the panel power output. It assumes power is Voc * Isc.Not sure what this has to do with the question about how well used panels work.
MPPT current is never going to be more than directly measuring current out of the panel outputs with an amp meter. And for the purposes of testing used (or new) panels, this works just fine.When you measure voltage and current at mppt, you get max power.
I wrote max power, not max current.MPPT current is never going to be more than directly measuring current out of the panel outputs with an amp meter. And for the purposes of testing used (or new) panels, this works just fine.
Keep in mind that panel warranties are usually 25yr, which means that after 25 years in service, they'll only be at least 80% of rating.
Especially for the price! Paying 80% less the cost of a new panel for a 10% hit in potential output? Yes please!
If you calculate like that, then nobody should ever buy used panels.Isc would be a simple and good way to determine degradation. Imp and power would be proportional to that.
It doesn't necessarily detect damage. I had a few where Voc and Isc were in family, but Vmp x Imp was less than half of good panels.
Quality undamaged panels will have great output even used. If price is right, a good deal.
Have to compare to 70% (after tax credit) of cheap new panels (assuming they are quality, something we aren't sure about), which we've bought between $0.17 and $0.30/W
Some panels have degraded badly. That could happen to new ones you buy. I looked for brands that held up well in reports of HAST highly accelerated stress tests, although not same model.