Just an EXAMPLE...
I run with LiFePO4 (LFP) Batteries which are 99% Efficient compared to Lead Batteries @ 88%.
A "Typical" 100AH LFP Battery can take up to 50A (0.5 C-Rate) for two hours to charge.
I have a Separate Charging system aside from the Solar & Other gear. Now I do have a fairly large battery bank at 1190AH but I use the separate charger @ 75A. To Charge my 24 Volt Battery Bank @ 75A, the Charger (94% Efficient, most are NOT) pulls 120VAC/23A.
Some quick numbers to put things into place.
NB, We suggest never exceeding 250A Draw from a Battery Bank. If you start reaching that level of draw, consider a Higher Voltage (drops Amps pulled) or using Paralleled systems.
12V/100AH = 1,280Wh/1.2kWh 4x100AH cells -4S BMS
24V/100AH = 2,560Wh/2.5kWh 8x100AH cells -8S BMS
48V/100AH = 5,120Wh/5.12kWh 16x100AH cells -16S BMS
We suggest typically to NOT exceed 250A Draw from a battery bank. Stacked Inverters extend that.
12V@250A=3000W (25A@120V, 12.5A@240V),
24V@250A=6000W (50A@120V, 25A@240V),
48V@250A=12,000W (100A@120V, 50A@240V).
(Uncorrected for inefficiencies) Excluding Surge Capacity Handling (High Frequency = X2, Low Frequency = X3)
Value Grade Inverters can be 82-88% Efficient. Tier-2 can be up to 92% while Tier-1 (Premium) can be up to 96% Efficient.