My inverters are definitely not designed to be synchronised, so I won’t be trying to do so, but the two alternatives you mentioned there are interesting and new to me. How much risk is involved in trying this, as i really have no desire to blow up or otherwise damage my €15,000 heatpump. However… to test if it will run on two mains phases is simple enough and I would wager the answer will be yes.Because it is VFD, should ramp up slowly so inverter doesn't have to supply a starting surge.
If it can run off two phases of the grid, maybe it can run from the "6000W" inverter, given a transformer to make 170V (of opposite phase) from 230V so it sees 400V between phases. And 230V from one phase to neutral. Or isolation transformer to make 200/400V split-phase.
What would I need to buy to test either of the two approaches you suggested there and is there risk involved or to the appliance would it be indistinguishable from 2 phases of a proper mains supply? Would there be any added strain on the inverter, save for the fact it’s now carrying the load the heatpump draws from both phase supplies?