Can the 18kpv grid support the 6000xp stack for a total of 24kW-AC?
I've played around with the 18Kpv using the 6000xp’s as the grid with on grid enabled. The 6000xps handle the surge loads on and off.
 
I am sorry about the confusions again! I was referring to "each" as a 4 panel group. I will try and again to clarify my logic. I will also post the panels below so you can see the specs.

I am installing a total of 16 panels. Each panel is giving me roughly 44 volts @ 10.2 amps totaling 450 watts. I am going to them all in groups of 4 (4 x 44v = 176 volts). This will give me 4 groups of 4 panels each totaling 16 panels.

Specs on the panels:
 
I am sorry about the confusions again! I was referring to "each" as a 4 panel group. I will try and again to clarify my logic. I will also post the panels below so you can see the specs.

I am installing a total of 16 panels. Each panel is giving me roughly 44 volts @ 10.2 amps totaling 450 watts. I am going to them all in groups of 4 (4 x 44v = 176 volts). This will give me 4 groups of 4 panels each totaling 16 panels.

Specs on the panels:
You need to use Voc not Vmpp for the safety limit (and maybe also start calculations)
 
I am sorry about the confusions again! I was referring to "each" as a 4 panel group. I will try and again to clarify my logic. I will also post the panels below so you can see the specs.

I am installing a total of 16 panels. Each panel is giving me roughly 44 volts @ 10.2 amps totaling 450 watts. I am going to them all in groups of 4 (4 x 44v = 176 volts). This will give me 4 groups of 4 panels each totaling 16 panels.

Specs on the panels:
I'd do two strings of 7 or 3 strings 6,6,4. What happened to the two panels? You said, "you had 18 panels".
 
I have 18 panels but I was under the impression 9 panels per inverter would be too much voltage.
If you have 2 mppt inputs per inverter then you can split up the 9 panels between the 2 inputs and you won't go over voltage.
You would go over voltage if you ran all 9 panels in series to 1 input.
 
If you have 2 mppt inputs per inverter then you can split up the 9 panels between the 2 inputs and you won't go over voltage.
You would go over voltage if you ran all 9 panels in series to 1 input.
Because 9 isn't divisible by 2 evenly, I would do one series of 4 panels and one series of 5 panels into each inverter?
Sorry, I just have so many more questions than answers lol
 
Last edited:
Hey guys. Can you do zero export grid tied with this inverter? I see it has a grid breaker and can pull power from the grid. Can it put power back to your main panel but not export it?
 
Because 9 isn't divisible by 2 evenly, I would do one series of 4 panels and one series of 5 panels into each inverter?
Sorry, I just have so many more questions than answers lol
I believe you can do it that way with this inverter.
If you want to play it safe, you can run 4 into input 1, and 4 into input 2 for inverter1. Then on the 2nd inverter you can run 5 into input 1 and 5 into input 2.
 
Hey guys. Can you do zero export grid tied with this inverter? I see it has a grid breaker and can pull power from the grid. Can it put power back to your main panel but not export it?
The only safe way to allow it to put power back to your main panel would be to backfeed power through a breaker in your main panel but you MUST use a generator interlock kit that would ensure the main/grid breaker and the breaker you are backfeeding with can NEVER be on at the same time. But yeah you could do that.
 
Hey guys. Can you do zero export grid tied with this inverter? I see it has a grid breaker and can pull power from the grid. Can it put power back to your main panel but not export it?

No, You would create a wiring nightmare if you try and get creative, it's a really bad idea to try and do an interlock if you are already tied, blah, blah.
 
No, You would create a wiring nightmare if you try and get creative, it's a really bad idea to try and do an interlock if you are already tied, blah, blah.
An interlock kit is fine enough as long as the inverter is providing enough power for all the loads. Otherwise you would have to power off some of your circuits to get the load down. I agree - a better idea is to use a transfer switch to be able to switch specific circuits between grid power and inverter power at will.

I would like to do a transfer switch but haven't gotten that far yet. In the meantime I'm using an off-grid (mostly) panel to power specific things, but with an interlock kit to be able to switch all the loads in the panel from the inverter to grid power for those times I need to take down my off-grid system for changes, maintenance, etc.
 