In February 2023, EG4 announced a significant change to how their inverters do grounding and bonding. Overall, these changes allow for much greater flexibility in installing the inverter in ways that are both supported and meet the NEC requirements for grounding and bonding. This document describes what was announced and goes into detail on how to use the information to properly set up a system using the EG4 6500 EX inverter.

This is the video they released to announce the changes.


In June 2023, EG4 released a single version of the firmware that allows the user to select Mobile or Stationary bonding behaviour

The new firmware versions are available at https://eg4electronics.com/downloads/

WARNING: The designs shown in the document are based on the information EG4 has provided. However, I have not personally tested all of them.

NOTE: Previously there was a similar resource that discussed both the EG4 6500 EX and the MPP 6548. This document replaces the EG4 portion of the older resource.

EDIT: 5 March 2023: Changed "Common Neutral Firmware" to "Stationary Firmware" in order to align with EG4 nomenclature.
EDIT: 23 July 2023: Updated document to reflect the new dual mode firmware.
  • Like
Reactions: bikerider4818
Author
FilterGuy
Downloads
399
Views
1,839
First release
Last update
Rating
4.80 star(s) 5 ratings

More resources from FilterGuy

Latest reviews

Excellent
Solved my biggest issue! Thank you so much.
Very Useful! Now I know not to bond the Neutrals on the outputs and I don't have to remove the neutral between the main breaker panel and the critical Load breaker panel!
Please explain how to tell which version (common neutral or mobile) you have. You say newer version will have the bonding screw removed. Does that change the firmware version? I bought my 2 inverters "day 1" when they were release. What do I have and what should I do now?
FilterGuy
FilterGuy
Thank you for the feedback. The new firmware is version 61.13 or later and is available at https://eg4electronics.com/downloads/