  1. F

    12V inverter with low consumption at idle

    I did a chat with Giandel and asked why they ship their 12V/1200W inverter with 5 AWG cables....They told me itwas tested, and if properly tighten, they are all good being only 2 ft long Very surprising...........and dangerous it seems !!!
  2. F

    12V inverter with low consumption at idle

    Would it be "safe" to use 2 AWG wires with the 12V/1200W Giandel inverter, knowing it won't be running continuously (the sump pump usually kicks in every 10min for ~30sec in the worst case scenario)? And in that case, what fuse should I use? Or are 2/0 AWG definitely required? And by the way...
  3. F

    12V inverter with low consumption at idle

    For their 12V/110V 1200W, Victron specifies 2 AWG on the manual....
  4. F

    12V inverter with low consumption at idle

    So to be safe, I should go with 2 AWG.....But not 2/0, right?
  5. F

    12V inverter with low consumption at idle

    Once the inverter's remote is activated by the sump pump switch......will it always stays ON?
  6. F

    12V inverter with low consumption at idle

    Nice file......thank you for creating it and sharing it The Giandel pure sine wave 1200W is apparently cheaper on the Giandel site than on Amazon.......
  7. F

    12V inverter with low consumption at idle

    When I put 12vdc, 120A and 3 feet, I get 4 AWG 4 AWG is the recommendation up to 160A For 165A, it shows 2 AWG So...................2/0 seems huge. Am I missing something?
  8. F

    12V inverter with low consumption at idle

    Any idea why Giandel includes a 6 AWG set of wires? It's also the size they specify in their manual .....! I understand the math you provided, but if 2/0 is what I should use, it seems very weird the manufacturer talks about 6 AWG
  9. F

    12V inverter with low consumption at idle

    Yes, but when the pump kicks in, the sensor will re-open quickly, and the pump will run on a timer
  10. F

    12V inverter with low consumption at idle

    From the link in your previous answer, the Giandel PS-1200JCR Pure Sine seems a good choice with low consumption at idle Will 4 AWG wires be ok?
  11. F

    12V inverter with low consumption at idle

    What would trigger that switch though?
  12. F

    12V inverter with low consumption at idle

    What would be your recommendation for a decent 12V inverter in the 1,200W range (to power a sump pump) that has a low power consumption at idle? Thanks
  13. F

    Automatic transfer switch between batteries

    Hello Assuming I have 2 x 12V batteries (A and B) that are different types and I don't want to have them in parallel (One is a new 100Ah LFP and the other one is an "older" 75Ah AGM but in good shape) Is there an module or circuit that would automatically switch from A to B when A has reached a...
  14. F

    Portable power station

    How are you wiring the 3 batteries in parallel? I see 2 fuses......and how does the smart battery sense work exactly?
  15. F

    Portable power station

    Hello, Is there any good tutorial to build a portable power station using 12V 100Ah mini batteries Redodo or Power Queen for example)? Could be 12V (2p) or 24V (2s2p) and will use the proper inverter accordingly Not sure what configuration would fit in such cases by the way...
  16. F

    LifePO4 outside?

    Hello I'm retrofitting some old solar garden lights to make them run out of 6VDC (2 leds in // and 47 Ohm resistors) Each lamp will draw ~0.75 Watts and I'm planning to have 10, so 7.5Wh But.....I don't want to run a 100 yard wire, bury it, etc... So I was thinking to have a LiFePO4 12V battery...
  17. F

    Redodo 12.8V 100Ah

    A 12.8V 100Ah Redodo LiFePO4 battery for $235 shipped.......is it a good deal?
  18. F

    Redodo inverters

    Has anyone tried the new Redodo power inverters (1000W and 2000W)?
  19. F

    Looking for a reasonably priced LiFePO4 battery...but "reasonably good" as well

    Is there any good tutorial you could recommend? And about the cells to buy, can you provide a link? I looked at the Qishou website, but redirect to Alibaba?
  20. F

    Battery disconnect

    Assuming I don't want to have the charger (Victron 12V/15A) permanently wired to the battery LFP 12V 100Ah), what type of battery disconnect/switch could I use? Would a 110V 2 pole switch work? If not, what are your suggestions? FYI, the positive wire is protected by an inline fuse.....
  21. F

    LFP charger for standby application

    Would this be a good choice (I like the possibility to manually switch the circuit) https://www.amazon.com/YOUNG-MARINE-Circuit-Trolling-Mount-50A/dp/B075KZTKDD or this: https://www.amazon.com/gp/product/B08ZXNZ3D3 with this: https://www.amazon.com/Conext-Link-AFS25-10-Nickel-Fuse/dp/B01D9ISXW6
  22. F

    LFP charger for standby application

    The pump's specs says 10A continuous and 18A in-rush...
  23. F

    LFP charger for standby application

    is 12 AWG enough?
  24. F

    LFP charger for standby application

    About the wiring, should it be A or B?
  25. F

    LFP charger for standby application

    Correct....not in conduit Any fuse holder suggestions with screw terminals?
  26. F

    LFP charger for standby application

    I'm not using an inverter nor pv..it's for a 12VDC backup sump pump So I need a charger that will maintain it in storage mode. Thinking about the Victron IP22 12V / 15A It doesn't come with wires, so I'm planning to use 10 AWG.... And I was asking for the fuse / fuse holder type. I know the fuse...
  27. F

    LFP charger for standby application

    Yes, this is why I mentioned the Victron... What about the wire size and fuse holder type?
  28. F

    LFP charger for standby application

    I think the 15A version does not.....
  29. F

    LFP charger for standby application

    Assuming I buy the Victron IP22 12v / 15A, it doesn't come with wires, so I will have to get some 1) I assume 10AWG are plenty enough for 15A? 2) I need to install a fuse, and it must be as close as possible to the positive battery terminal, correct? 3) What type of fuse / fuse holder should I...
  30. F

    LFP charger for standby application

    So better go with a Victron charger, right?
  31. F

    LFP charger for standby application

    Hello, Other than Victron, what chargers have a storage function (to maintain the battery at a reduced voltage once fully charged) About Victron: other than the IP (22 vs 67 and the 15A vs 17A), are there any major differences between...
  32. F

    Looking for a decent inverter

    So it means 1/0 AWG + 125A would be.................just fine?
  33. F

    Looking for a decent inverter

    Ok for the MRBF fuse...how many amps should I get for a 2/0 AWG ?
  34. F

    Looking for a decent inverter

    Thanks for the Windynation link So better go with something like that for the fuse...
  35. F

    Looking for a decent inverter

    Assuming I go with a 1000W or 1200W inverter, and get the 2/0 AWG Harbor Freight cables: https://www.harborfreight.com/3-ft-20-awg-inverter-cable-set-63748.html Am I good with a breaker like this one: https://www.amazon.com/dp/B0BK327G4D/ref=twister_B0B2RM3TPF?_encoding=UTF8&th=1 Should I go...