    Terminal Damage - Proper Connection - LifePo4 with Flexible Bus Bars

    Terminal, bus bar, bms ring terminal, washer, nut is the sequence used.
  2. L

    Terminal Damage - Proper Connection - LifePo4 with Flexible Bus Bars

    Appreciate the direction. About 10 amps, that was blowing fuses. 30 amps for charging. I'll monitor with the smart shunt and full load test.
  3. L

    Terminal Damage - Proper Connection - LifePo4 with Flexible Bus Bars

    So perhaps it was just one bus bar not torqued and remainder factory welding. Will do!
  4. L

    Terminal Damage - Proper Connection - LifePo4 with Flexible Bus Bars

    Thanks! Didn't notice it when installed a year ago, so felt like a gut punch. Will reset the battery and check.
  5. L

    Terminal Damage - Proper Connection - LifePo4 with Flexible Bus Bars

    These terminals appear to be arcing or even melting. This battery saw very light duty for a short period while testing minor electrical components, but will drive an electric vehicle at far greater loads. I wire brushed black residue off the terminals before taking the picture. The terminals...