6000XP's -2 of them. 4000wats MAX ALLOWABLE, per MPPT, 480VDC MAX ALLOWABLE per MPPT - 2 MPPT's per XP
Below figures based on ONE MPPT's input maximums.
8 - 455 watt panels, per MPPT = 3640 watts, per MPPT, voltage = 394VDC.
On a 15 degree day, voltage increases to 435VDC, MPPT MAX ALLOWABLE 480VDC. (OK here I assume)
Total watts per MPPT (15 degree day), (V x A) = 435VDC X 10.96A = 4767 watts. MAX ALLOWABLE per XP, BOTH MPPT's = 10,000 watts, 5000 watts each, (I assume) as per manual.
Subtract 4VDC for voltage drop (150' run, 10ga PV wire) = 431VDC x 10.96 A = 4723 watts, per MPPT.
XP's MPPT's track best between 120 and 385VDC
Could I have matched the panels to the MPPT's better?