I'm building out a 800w 12v off grid solar setup for a small cabin with Victron components (Muliplus ii, Lynx, Cerbo & 406amh Epoch 12v). I have 4/0 running from batteries to invertor and invertor to Lynx. Only 2/0 fits on the chassis ground of the MPii to the lynx. I had planned on using 4/0 to ground to a ground plate outside of the cottage but it doesn't look like they accept that high of gauge. So that has me rather stumped....
The 3000/12/120 manual shows a 12AWG for the ground, but I'm going to assume that's just a chassis ground.
I'll have DC running to a distribution panel and AC to on Out1 to a 50amp panel (with no ground).
Any idea's on how I can ground the system via the lynx? Everything I've read says the wire should match power source. Any help would be much appreciated.
I'm building out a 800w 12v off grid solar setup for a small cabin with Victron components (Muliplus ii, Lynx, Cerbo & 406amh Epoch 12v). I have 4/0 running from batteries to invertor and invertor to Lynx. Only 2/0 fits on the chassis ground of the MPii to the lynx. I had planned on using 4/0 to ground to a ground plate outside of the cottage but it doesn't look like they accept that high of gauge. So that has me rather stumped....