Theory and Seriousness, all a learning process.
I have a Huawei 10K inverter, SUN2000 - 3.857.691011.4KTL-USL0 (10K model) that has 3 PV input lines (for 3 PV arrays) each rated at 15amps. I'm only using 2 at the moment, with two arrays of 15 panels each array with Power Optimizers on each panel (QPLUS_L_G4_2_335-345_2017-01 panels). I'm on a GRID based "On Demand" plan, which, tracks the highest demand between 4pm and 7pm and uses that value to determine the electric bill. If you can limit your total DEMAND rate during this time, electricity is very, very cheap at ALL times, even during PEAK. It's that damn DEMAND multiplier.
In the real world, there's Dinner to be made (ovens and such), clothes to be washed, dishes to be cleaned, TVs to be powered on, Computers to be powered on, all at times right at peak, 4pm to 7pm when everyone is getting home.
If, somehow, you had a "buffer" of stored energy that can be tapped into during this window, you could limit the GRID demand load. Just enough to prevent the PEAK spikes during ON PEAK hours.
All 3 inputs of my GTI have a minimum of 360v with a max of 600v with a 15amp limit. If I can control the 3rd input so voltage is only available on that 3rd input between 4pm and 7pm, that means, I can connect my battery bank to the 3rd input and it only draws for that time, the batteries can be used to supplement the solar to handle the boost in Demand for that time frame, thus reducing my DEMAND charge from the GRID, lowering my entire bill.
Outside those hours, the battery bank would be disconnected from the GTI via relay. The Batteries are connected to individual 2A chargers plugged into my Electric Panel via relay as well. I use GRID power to charge the batteries back up before the next cycle. The Relays are inverted to each other (either or), so they can never be ALL OFF or ALL ON, they are always opposite. Again, electricity is CHEAP but it's that DEMAND multiplier is the counter for that.
The issue isn't HOW much electricity you use, it's how much you pay for each KW used. The ON DEMAND rate is SUBSTANTIALLY cheaper than any other rate per KW from the GRID because they know they are going to make up for it using the DEMAND modifier. If you can make your peak DEMAND remain close to 0 or 1, your bill is next to nothing. I can use 1,000Kw and my bill is like 20 bucks (exaggerated yes).
Yeah, you can shut off appliance, don't do this, turn this off, etc, etc. However, if you didn't want to force changes in your daily routine, this seems to be the ticket. I don't want a Battery Backup, I want a Battery Filler.
A slew of questions comes pouring in.
1. WiIl the sudden "inrush" of voltage and current" blow through the inverter?
2. Does the Inverter limit the input to 15amps or will the Inverter start sucking in AS MUCH as the battery can give until either the Battery or Inverter goes BOOM? The manual says each PV array is 15A max, but, it doesn't say you have to configure panels to stay under that. I mean, if you add more panels to adjust for "loss" or similar shading, I have to beleive even if the PV array can exceed 15A the Inverter will run away with it?
3. Finding anything that gracefully handles 480V, even tho limiting to 15amps, is a challenge. There is a relay, HDD-6V20E-HS1.0U , https://www.power-io.com/products/hdd.htm, that handles it, but, there's still the inrush?
4. Since the GTI is an MPTT device, I think it's looking for a gradual "ramp" of voltage. Again, finding something that can handle 480v DC is akin to Frankenstein's Castle laboratory.
Granted, 480V DC from a bank of batteries is some serious stuff, but, why should the GTI care if the Voltage is coming from Batteries, a PV Grid Array, a Windmill, a water wheel, or some kid peddling a bike with a generator on it? All it cares about is converting DC Voltage to AC, and if you can get DC Voltage to it's input, it will convert it?
Help?
I have a Huawei 10K inverter, SUN2000 - 3.857.691011.4KTL-USL0 (10K model) that has 3 PV input lines (for 3 PV arrays) each rated at 15amps. I'm only using 2 at the moment, with two arrays of 15 panels each array with Power Optimizers on each panel (QPLUS_L_G4_2_335-345_2017-01 panels). I'm on a GRID based "On Demand" plan, which, tracks the highest demand between 4pm and 7pm and uses that value to determine the electric bill. If you can limit your total DEMAND rate during this time, electricity is very, very cheap at ALL times, even during PEAK. It's that damn DEMAND multiplier.
In the real world, there's Dinner to be made (ovens and such), clothes to be washed, dishes to be cleaned, TVs to be powered on, Computers to be powered on, all at times right at peak, 4pm to 7pm when everyone is getting home.
If, somehow, you had a "buffer" of stored energy that can be tapped into during this window, you could limit the GRID demand load. Just enough to prevent the PEAK spikes during ON PEAK hours.
All 3 inputs of my GTI have a minimum of 360v with a max of 600v with a 15amp limit. If I can control the 3rd input so voltage is only available on that 3rd input between 4pm and 7pm, that means, I can connect my battery bank to the 3rd input and it only draws for that time, the batteries can be used to supplement the solar to handle the boost in Demand for that time frame, thus reducing my DEMAND charge from the GRID, lowering my entire bill.
Outside those hours, the battery bank would be disconnected from the GTI via relay. The Batteries are connected to individual 2A chargers plugged into my Electric Panel via relay as well. I use GRID power to charge the batteries back up before the next cycle. The Relays are inverted to each other (either or), so they can never be ALL OFF or ALL ON, they are always opposite. Again, electricity is CHEAP but it's that DEMAND multiplier is the counter for that.
The issue isn't HOW much electricity you use, it's how much you pay for each KW used. The ON DEMAND rate is SUBSTANTIALLY cheaper than any other rate per KW from the GRID because they know they are going to make up for it using the DEMAND modifier. If you can make your peak DEMAND remain close to 0 or 1, your bill is next to nothing. I can use 1,000Kw and my bill is like 20 bucks (exaggerated yes).
Yeah, you can shut off appliance, don't do this, turn this off, etc, etc. However, if you didn't want to force changes in your daily routine, this seems to be the ticket. I don't want a Battery Backup, I want a Battery Filler.
A slew of questions comes pouring in.
1. WiIl the sudden "inrush" of voltage and current" blow through the inverter?
2. Does the Inverter limit the input to 15amps or will the Inverter start sucking in AS MUCH as the battery can give until either the Battery or Inverter goes BOOM? The manual says each PV array is 15A max, but, it doesn't say you have to configure panels to stay under that. I mean, if you add more panels to adjust for "loss" or similar shading, I have to beleive even if the PV array can exceed 15A the Inverter will run away with it?
3. Finding anything that gracefully handles 480V, even tho limiting to 15amps, is a challenge. There is a relay, HDD-6V20E-HS1.0U , https://www.power-io.com/products/hdd.htm, that handles it, but, there's still the inrush?
4. Since the GTI is an MPTT device, I think it's looking for a gradual "ramp" of voltage. Again, finding something that can handle 480v DC is akin to Frankenstein's Castle laboratory.
Granted, 480V DC from a bank of batteries is some serious stuff, but, why should the GTI care if the Voltage is coming from Batteries, a PV Grid Array, a Windmill, a water wheel, or some kid peddling a bike with a generator on it? All it cares about is converting DC Voltage to AC, and if you can get DC Voltage to it's input, it will convert it?
Help?