Almost, there will be a whole house disconnect or grid breaker between the meter and 18k.Having issues finding a definite answer. Is it possible to go straight from the meter to the 18kpv and then to the main panel?
Almost, there will be a whole house disconnect or grid breaker between the meter and 18k.Having issues finding a definite answer. Is it possible to go straight from the meter to the 18kpv and then to the main panel?
Awesome. I assumed I should have the PV disconnect, and rsd installed also. Is there any chance for export in this scenario? Do I even need to alert my power company?Almost, there will be a whole house disconnect or grid breaker between the meter and 18k.
yes.I assumed I should have the PV disconnect, and rsd installed also.
With an 18kpv, there will likely be some export regardless of your settings. When a large load suddenly cuts off, the power has to go somewhere.Is there any chance for export in this scenario?
18kpv: Probably. 6000xp: I can make the argument that it is no different than a battery charger to the grid.Do I even need to alert my power company?
Not correct.With an 18kpv, there will likely be some export regardless of your settings.
You’re operating in parallel even with zero export mode. This generally requires an interconnection agreement (interconnection does not imply export).Do I even need to alert my power company?
I have a question about the 200AMP pass through. In the 18k PV diagram it shows 60 AMP breakers. How does the 200AMP pass through work with a 60 AMP breaker?
NEC only allows 160A continuous (80%), so I don’t see a problem with this. Other than confusing documentation/bad copy pasteAgain, total confusion. EG4 needs to create better schematics. Show us a schematic that can use the full 200A bypass that you market.
You can start scrolling at page 33. Many whole house backup options. Not sure which specific tie in you wanted.post the link please
Easy bypass if the inverter goes bad.Yep, saw them. Why the manual transfer switch?