Nice. Can you link to the breakers? Never heard of those. Any DIN breakers that can handle 400VDC need to be on our list.I went with a Square D box ($13) and Nader 400vdc breakers ($15) and a din rail from Grainger ($3.50).
View attachment 12522
Nice. Can you link to the breakers? Never heard of those. Any DIN breakers that can handle 400VDC need to be on our list.
Thanks. 60VDC is not high enough for me. But, I do need a cheap outdoor box just for running my PV cable through for my panels. A lot of people run their combiner box to the panels, but cuz of the price of 4 AWG vs 10 AWG, and the convenience, the combiner box and the panels are far apart. So, I need an outdoor box just for running PV wires to that's very close to the panels. Your Square D box is perfect for that!My bad, only 60VDC.
ASI 20 Amp 240Vac/60Vdc Miniature Circuit Breaker DIN Rail Mount
ASI 20 Amp 240Vac/60Vdc Miniature Circuit Breaker DIN Rail Mount NDB2-63C20-1 - The Home Depot
The NDB2-63C20-1 Miniature Circuit Breaker, MCB, is rated at 20 Amp at 240 VAC and 60 VDC. This single pole circuit breaker has a superior 10kA interrupt capacity, an easy to wire shock proof wire terminations,www.homedepot.com
Here's the box.
Square D QO 60 Amp 240-Volt 7.4 kW Non-Fuse AC Disconnect
Square D QO 60 Amp 240-Volt 7.4 kW Non-Fuse AC Disconnect(QO200TRCP) QO200TRCP - The Home Depot
For more than 90 years, we've been the unchallenged leader in safety switches. Our Square D brand safety switches are preferred two to one over our closest competitor. We've continued our tradition ofwww.homedepot.com
Not an electrician, but i assume this is a single pole breakers, so which wire, positive or negative, attaches to it? I have 4 - 100W panel in series each produce 6 amps, 4 x 6 = 24, so I'm assuming a 30a breaker, right?This is a very interesting thread! My LV2424 Hybrid is on it's way. I agree for the price point it can't be beat!
A breaker between your panels and MPP is a good idea as it serves to both protect your system and act as a PV disconnect. Your panels should be the first thing you disconnect and the last thing you reconnect when you service your system. Flipping a handy breaker makes that super easy. YOUR breaker should be sized a panels in seriesccording to your panels. If your panels generate 7 amps each and you have two in series that's 14 amps and a 15 amp breaker will work. I have 17 amps protected by a 20 amp breaker in my system. Make sense?
Man. This thread has me rethinking my component build...I’d be spending about another $2-300 to get the Hybrid LV2424, but the simplicity and compact form factor are really swaying me in this direction...Can anyone push me over the edge in one way or another?
Not an electrician, but i assume this is a single pole breakers, so which wire, positive or negative, attaches to it? I have 4 - 100W panel in series each produce 6 amps, 4 x 6 = 24, so I'm assuming a 30a breaker, right?
Never mind, just needed a .rar unpacker.Any tips installing the software? I can't find the install icon and the Windows folder on the disc is a .rar file.
I don’t have anything going into the unit what so ever. I have 8 solar panels and it gave me a reading of 80 volts when I had all of them plugged in. I was running two 400 watt arrays in parallel getting 80volts. I ended up unplugging two of the panels, leading me to have a total of two 300 watt arrays in parallel but now it is only reading 28volts so at this point I am royally confused. My voltage on my batteries is 26.8 currentlyMade sure the power saving mode is disabled ( screen 2) Do you have 120 volt AC connected to the unit?
Are you sure you unplugged a panel from each array? Or did you unplug 2 panels from the same array? If you did, that would make one array half the voltage of the other, and combining different voltages in parallel is a big no no that can cause a funky voltage reading.What I’m wondering is how my array went from being 80volts to 28??
Sed linked to an ASI breaker on homedepot.com, but they sell directly, and have DC breakers rated at 125vdc/pole. Using a two-pole breaker on positive and negative, according to the datasheet, would give up to 250vdc. Here's an example, a two-pole 50A breaker at 250vdc:Any DIN breakers that can handle 400VDC need to be on our list.
Very nice find. Added to my breakers page.Sed linked to an ASI breaker on homedepot.com, but they sell directly, and have DC breakers rated at 125vdc/pole. Using a two-pole breaker on positive and negative, according to the datasheet, would give up to 250vdc. Here's an example, a two-pole 50A breaker at 250vdc:
Electronic Components & Supply Online Store | ASI
Need automation components and parts? Check out ASI's vast inventory of electronic components for automation and industrial applications.www.asi-ez.com
Quite a difference between 250vdc and 400vdc, but 250vdc isn't nothing.