My garage is on the opposite corner of the house, almost all of the high-current loads are located there, so I am considering putting in a subpanel with battery backup. I may add solar, but that would likely be AC-coupled, unless there's some advantage to running it into the inverters directly. What I would like to do is utilize a pair of existing 50A 240V lines that run to the exact spot where I would put the inverters and panel.
Can I connect each of the 50A lines to an 8-10kW (6kW might work as well) parallel-capable inverter, connect the outputs in parallel, and draw more than 50A from the output in passthrough mode and/or in battery mode? Will they load balance between the inverters to split the load? Can I charge a battery bank from the pair of inverters as well with it balancing the load?
If the answer is yes, then any suggestions on inverters to consider or avoid would also be apricated if someone has experience running in such a configuration. The inverters would need to be split-phase 240V output, but most of the load is 240V, so balancing the 120V legs should not be too much of an issue.
FWIW, it may or may not be grid-tied, depending on what I end up doing with the solar. I don't think the battery has to be grid-tied, though.
TL;DR: Do parallel inverters balance load across their AC inputs so that the combined total output can exceed the load capacity of the inputs individually? Is that code compliant, or is it equivalent to connecting two circuits together to try to get more capacity? My assumption is that each inverter could be configured to not draw more than 50A (or 40A if it has to be derated), so there wouldn't be an issue with overloading one line if the other disconnects.
Can I connect each of the 50A lines to an 8-10kW (6kW might work as well) parallel-capable inverter, connect the outputs in parallel, and draw more than 50A from the output in passthrough mode and/or in battery mode? Will they load balance between the inverters to split the load? Can I charge a battery bank from the pair of inverters as well with it balancing the load?
If the answer is yes, then any suggestions on inverters to consider or avoid would also be apricated if someone has experience running in such a configuration. The inverters would need to be split-phase 240V output, but most of the load is 240V, so balancing the 120V legs should not be too much of an issue.
FWIW, it may or may not be grid-tied, depending on what I end up doing with the solar. I don't think the battery has to be grid-tied, though.
TL;DR: Do parallel inverters balance load across their AC inputs so that the combined total output can exceed the load capacity of the inputs individually? Is that code compliant, or is it equivalent to connecting two circuits together to try to get more capacity? My assumption is that each inverter could be configured to not draw more than 50A (or 40A if it has to be derated), so there wouldn't be an issue with overloading one line if the other disconnects.