I charged the batteries via Utility/Grid yesterday night to SOC 90% by changing the parameter 6 temporarily (to Utility can charge batteries if Solar power is not available) and it charged fine.
The inverter is still working in a bypass mode ie taking the power from the grid only because the...
At Inverter I’m getting as below -
Voltage 135V (both while connected to the Inverter’s terminals as well as open circuit)
Current 16.9 (Open circuit only)
See attached pictures. This test confirms that all connections from the panels to all the way to the inverter are good.
Alright, I installed the SolarAssistant yesterday. Fairly easy (took 1 hour from start to end). I was not sure which inverter type to select and that is the item took little longer.
Back to the fault code 14 issue -
When microwave is run today, the following was the load on each phase. Phase 2...
I have put 7 panels in series last night and the voltage at the inverter is 320V. The Inverter display is reading around the same amount. The amps are still 0 on the inverter.
But not sure why Short circuit amps are around 40 amps. This seems high as in series only voltage adds up and current...