diy solar

diy solar

Recent content by Robbert

  1. Robbert

    JK-BMS says 3.317V per cell but only 3% SoC

    Just replaced a JK Bms for a spare one and the SOC is totally not right. I know that because the other one in parralel is pretty accurate. Every cycle it gets better. After a couple of charges (to full), it will give you the right SOC. Depending on how often you hit 100% it can take some time.
  2. Robbert

    Do I need bus bars?

    I use Victron Lynx power in. Not very expensive (you get 2 busbars in one case). It helps you to build a clean installation. Also if you want to add more to your system, it provides some flexibility. Maybe not necessary, but i would definitely go for busbars.
  3. Robbert

    How many relays (split phase)

    Thanks for your feedback. I'll start searching for a 2 pole din relay
  4. Robbert

    How many relays (split phase)

    Hi, I would like to isolate my inverter from AC-in, and only allow AC-in if that is neccesary. The reasons why I want this are: 1) the inverters that I use, use AC power if connected to the grid. If disconnected they use from the battery/solar 2) we have a very instable grid and after outages...
  5. Robbert

    Battery Bank per Inverter

    What you want is fine, but you still might want one shared bank. I had a setup like you described but changed it by paralleling the batteries in one large bank. Paralleling the batteries, effectively make one large battery, and connect the inverters/chargers to this large battery could be more...
  6. Robbert

    What Class T fuse for my Ruixus ?

    Indeed getting matching fuses is important. I found out the hard way :)
  7. Robbert

    What Class T fuse for my Ruixus ?

    I purchased the Blue Sea fuse block with matching fuses. For your reference I added a couple of pictures that show the differences between the two kinds.
  8. Robbert

    What Class T fuse for my Ruixus ?

    Had those as well. They might be perfectly fine. However after comparing these fuses with other class-t fuses, I replaced them. The fuse block and the fuses themselves are just a world of difference compared to other class-t fuses and blocks. These ones are small and flimsy.
  9. Robbert

    Vertical Battery Case with wheels

    I read those discussions as well and based on that, I always though it's better to keep them straight up. However many battery manufacturers nowadays offer vertical boxes with this layout. So apparently it's not too bad. Maybe in the long run, over years, it might affect the cells. Bought...
  10. Robbert

    Battery Bank Size

    You are right. A balancer does not make any sence to add to batteries in parallel.
  11. Robbert

    DIY battery longevity

    It doesn't have to be much higher than 3.45. I charge to 55.8 (3.48) per cell. Absorbtion is 30 minutes and usually there is a deviation at the end of absorbtion, smaller than 5Mv. I use B-Gade REPT cells and have approx 200 cycles.
  12. Robbert

    Midnite Solar Announced their new 10kw AIO at Intersolar Today

    It is my understanding that some Voltronic inverters (like mpp solar pipMax) do deliver back very small amounts, even if not reported in de app/SA.
  13. Robbert

    CHINS 12V 300ah LiFePO4 reading over 17 volts

    I would not use that battery. That's over 4 volts per cell and ready to fail.
  14. Robbert

    Voltage through dry contacts (BMS)

    Thanks, couldn't find that in the documentation from JK. To be on the safe site, I think Ill get one that allows 12v DC, as control voltage. Only consequence, in that case, is that I need to get a dc to dc stepdown converter as well. 12volts sounds much safer anyway. ..
  15. Robbert

    Voltage through dry contacts (BMS)

    I would like to program and use the dry contacts in my new JK-inverter BMS. The purpose of this is to control a relay that switches AC-power-in to the inverter to 'ON' if the battery gets below a certain SOC. That way the inverter is disconnected most of the time from the grid and only has...