Not quite! The circuit's smallest wire gauge determines the breaker rating.
New work:
You must look at the entire circuit & calculate the amperage requirement for all appliances. Now run the appropriate gauge wire & attach to an appropriately rated breaker.
Remodeling:
Determine the circuit...
You might see an improvement using an Easy Start device. They are pricy but very effective, it can lower surge current by as much as 70%.
I'm a very satisfied customer I can start & run a 15K RV AC unit on a EU2200Si Honda in ECO mode, with other minimal loads running.
I would say a finer resolution ie. more mv deviation per amp. A 100mv 100 amp shunt is 1:1, a 50mv 100 amp shunt is 0.5:1.
The resistive material the shunt uses is more related to its accuracy than its mv rating.
If you have access to each cell (a true wet lead acid battery) get a real hydrometer with the three glass float made for battery maintenance. They are rather inexpensive. Then charge them up and let them rest an hour or 2, then record the specific gravity & temp for each cell.
This will reveal...
Then consider an RV type 12VDC diaphragm pump. It eliminates the need for an inverter.
Shurflo 2088-554-144 Fresh Water Pump, 12 Volts, 3.5 Gallons Per Minute, 45 Psi
Plus a bladder tank accumulator to suit.
WaterWorker HT-2B Water Worker Vertical Pre-Charged Well Tank, 20 Gal, 3/4 In Mnpt, 100...
Not connected to a load is not a problem.
To balance a flooded lead acid battery you must do an equalizing charge. (You must have access to each cell. Maintenance free batteries are not candidates for balancing.)
Fully charge the battery.
Test each cell for specific gravity
Note the readings...
If they are pre-assembled they should come with an internal BMS
Yes
???
Parallel requires an even count of panels. 2, 4, 6, 8 works where 3, 5, 7 will not work or requires a second SCC due to voltage mismatch..
I'd purchase an additional panel if there is room or return one if no room for the...
I'm afraid it is not Arduino friendly. There may be a version in my future that is though.
I'll be starting a project next year to monitor PV performance with Arduino.
You buried the propane tank, I'd consider doing the same for the battery box even if indoors (beneath floor or root cellar) Then plumb up a propane line to it & install a space heater in the space & just use the pilot to heat the battery space. Even that may prove a bit excessive due to the...
Point 4: a grid supplied charger will never rest (24/7/365) charging. A SCC takes a break when the sun goes down & depending on the model can be tailored to your needs.
You are correct, & many batteries are sold. My Progressive Dynamics PD9270V Inteli-Power 9200 Series Converter/Charger with Charge Wizard - 70 Amp bulk charges @ 14.2V, absorb charges @ 13.7V, & floats @ 13.2V. Going on 8 years continuous duty with 3 GC-135 FLA batteries with a high impact wreck...
I believe your concern is well placed. I would prepare shoring to support the roof & stabilize the walls.
Once you get the inner skin off, NO MORE DRIVING!
@dt1400 If you indeed swap out your inverter, I'd be interested in it. Only if you make the swap & are satisfied with the results. I assume you'd return the 2K unit if it fails to work out.