  1. T

    Inverter generator terminals

    Yes and no. Yes, the transfer switch will switch between them. But the port would have to be reconfigured each time you switch it.
  2. T

    Cool text this morning from customer

    Those long exposed bus bars are scary.
  3. T

    Can somebody help me how to do neutral to ground bonding on POWMR 10.2kw hybrid inverter ?

    Test at the inverter output. You have to disconnect the wires from the inverter. Otherwise you are not just testing the inverter.
  4. T

    Can somebody help me how to do neutral to ground bonding on POWMR 10.2kw hybrid inverter ?

    Good Not good This doesn't make sense. Are you using a digital multimeter?
  5. T

    Can somebody help me how to do neutral to ground bonding on POWMR 10.2kw hybrid inverter ?

    That's fine. Ground is Ground. There's no difference between input and output.
  6. T

    new unused 12V 400A eg4 server rack battery

    Use the "report" function. And the staff can remove it for you.
  7. T

    EG4 6000 XP - Splitting Out the 240 Split Phase Into 2-120V Circuits

    If that's the case, then just do it at the panel. And yes, you can only have one N/G bond.
  8. T

    Open Ground on Power Strip and GFCI

    If it's just a temporary use thing. This would be fine. If a permanent use at the location, a more permanent solution would be better.
  9. T

    EG4 6000 XP - Splitting Out the 240 Split Phase Into 2-120V Circuits

    Run the L1, L2, N, and G from the 6kxp to the service panel. You will have to check if the 6kxp takes care of the N/G bonding. This should be the default, but you never know. If not, then you will need to do it in the panel. The service panel can be a main lug type, as there's already a...
  10. T

    EG4 6000 XP - Splitting Out the 240 Split Phase Into 2-120V Circuits

    Install a sub panel and feed whatever circuits you need.
  11. T

    new unused 12V 400A eg4 server rack battery

    Not sure if you realize that you posted in the wrong section. This one is for solar panels. You want....... https://diysolarforum.com/forums/batteries-for-sale.40/
  12. T

    The Devil's Dictionary of PV Jargon

    That's entirely too much effort for a laugh. lol
  13. T

    Combining wire in junction box

    Yes It doesn't matter if it's AC or DC. Unless you are trying to disconnect under load.
  14. T

    Can somebody help me how to do neutral to ground bonding on POWMR 10.2kw hybrid inverter ?

    You need to disconnect the output wiring. Not just turn it off.