EG4-6500 system starting 4 ton A/C

Here's a couple of pictures of the setup. In short, my main panel is in another room, so I had to run power to a sub panel, seen on the right next to the battery bank - which feeds the inverters, which feeds the off-grid panel to the left. That panel just feeds loads that I've added new, or moved over from the main panel.

View attachment 149447

A large bundle of cables come from the main panel to that area in the top left of the below picture - if moving a load, I just turn breaker off in the main panel, cut the wire, cap it, and then add it to a JBox that connects the load to the off-grid panel below. In this case, since this happened late last night and I had to move my AC unit back to the main panel, I just spliced it back together with WAGOs and taped it up temporarily until I can get it either put in its own Jbox, or back to the off-grid panel, spliced in a separate Jbox out of the picture.

View attachment 149445

The two orange cables are for moving the AC units off-grid. The one on the left is reserved for AC1, a bigger 4 ton unit that I just pre-ran the wire to the Jbox above where I'm standing and the one on the right is for AC2, a smaller 2.5 ton unit.

But as you can see by the burn mark on the concrete backer board, it definitely didn't like the hot leads to the load swapped for some reason - though it also didn't work the other way either. Either way, I figured I could at least put this out there for others to learn from once I figure it out.
Very clean setup. Good job!
 
I wonder how well the soft starts work with loads other than AC. I read that they aren’t ideal. Am thinking that I might use 3-phase motors and VFDs on anything over 4-5 hp. Biggest two would be an air compressor and dust collector. And possibly a European Joiner/Planner combo.

I have four Sunny Islands that should be able to handle a lot, but I don’t want to hammer them if I can avoid it.
 
I wonder how well the soft starts work with loads other than AC. I read that they aren’t ideal. Am thinking that I might use 3-phase motors and VFDs on anything over 4-5 hp. Biggest two would be an air compressor and dust collector. And possibly a European Joiner/Planner combo.

I have four Sunny Islands that should be able to handle a lot, but I don’t want to hammer them if I can avoid it.
My soft starter should be here in the next ten days. Once I install it I'll give you some feed back on how it does.
 
Do you have to pull the pump or will it wire in at the contacts?
Either at the contacts or in the load panel. I put it in it's own metal box close to the pressure switch. It does get warm so I wanted it isolated. I have a 3/4 HP 240V pump and they sent me an SL22 4R014.
 
My soft starter should be here in the next ten days. Once I install it I'll give you some feed back on how it does.
Got my soft starter in. Works like a dream. It pulls a hair more them my 1 hp well pump but less then my stove. Only hitting 30% on both inverters. Usually only at 6% for normal house. Lights, fans, and ect
 
Congrats! your wife will love you even more with all the new AC!
Now we need more sunshine to recharge EG4's. They are hungry for Photons!
 
Got my soft starter in. Works like a dream. It pulls a hair more them my 1 hp well pump but less then my stove. Only hitting 30% on both inverters. Usually only at 6% for normal house. Lights, fans, and ect
Update. Once the house gets to temp, the inverters are at less than 20% I've been amazed at how well it works. I'll add a pic so you can see the footprint.
 

Attachments

  • 20230520_152109.jpg
    20230520_152109.jpg
    119.1 KB · Views: 14
I’m having an issue with my two split phase 6500s and a 2.5 ton. I have it on the micro air soft start which measures the the start up amp at 21amps. The heat pump alone is not a problem but when I added the air handler it dims and blinks the light whenever it starts up for about 2 seconds. Does an air handler need a soft start?

I have 10kW of solar and 55kW of battery storage. I also changed my settings to allow both 6500s to pull 150amps each from the battery banks. Any recommendations?
 
The squirrel cage motors in air handlers that are typically psc motors will have close to locked rotor amps when started can be an issue. In mine I replaced with a variable speed motor ( ecm ) with a controller to adjust airflow to my duct work and it's also setup to be two speed, low for 15 minutes and automatically goes to the second speed if demand requires more air flow

This is one that doesn't need a controller and is an ECM ( ramp up to speed over ~20 - 30 seconds ) and is very simple to hook up / replace as motor air handers use the same frame size for the motors. Here is the manual

Another benefit is ECM is very efficient where psc motors use a capacitor to slip the phase for difference speeds, all the same power draw just wastes energy.
 
The squirrel cage motors in air handlers that are typically psc motors will have close to locked rotor amps when started can be an issue. In mine I replaced with a variable speed motor ( ecm ) with a controller to adjust airflow to my duct work and it's also setup to be two speed, low for 15 minutes and automatically goes to the second speed if demand requires more air flow

This is one that doesn't need a controller and is an ECM ( ramp up to speed over ~20 - 30 seconds ) and is very simple to hook up / replace as motor air handers use the same frame size for the motors. Here is the manual

Another benefit is ECM is very efficient where psc motors use a capacitor to slip the phase for difference speeds, all the same power draw just wastes energy.

Looks like my system is actually a 2 ton system. I actually just put in a new air handler motor last year, so I have the motor specs (see below photos.)

I calculated:
1/5 HP = 0.2
CL:B = 3.54kva
3.54 X 1000 X 0.2 = 708
708 / 240v = 2.95
2.95 / 1.73= 1.7 startup amps

if my math is correct, it doesn’t seem like it is adding much work to the inverters.

I tried swapping breakers. I used all mini breakers in my sub panel however, it seems the mini breakers can't handle the surge. I'm assuming its because it has less contact with the bus bar and can't draw enough current during a surge. At least it was an easy fix.

Thanks and regards,
 