Complete guide for 48V using EG4 18k

All I want to do is fill my batteries, and the sun doesn't want to come out and play this week. There are load shifting settings with some clock times you can set, never used it. SRP is 5-9,5-9 APS is 4-7P. Load shifting right now is almost a joke with the 0.03/KWH spread, the charge/discharge loss will remove any cost benefit, but should give you time to play with the discharge settings. Similar deal in summer here, with 2-8 or 3-8. Sun is killing it you should have your batteries maxed out by the time the sun goes down, let them fly until they are empty, Probably won't cover the gap unless you have around 30KWH. The point is force charging/discharging batteries has little benefit from a $$$ perspective here in Phoenix. You will be maxing out Solar production when TOU starts, and the batteries will last you for however long into the evening once the sun sets. Places with higher winter spreads might benefit, but you'll get all your summer benefit without even trying by the nature of the TOU timing tracking sunshine with a ~2-3 hour delay.

Last summer I found that 30KWH sometimes did not get me thru until 8PM, even when at 100% SOC by 1300. YMMV
Yep this was a tough week to start my system. Had a solaredge without battery for 5 years. Designed all my solar systems and picked EG4 on price since the savings over solark covered the first 14kw battery, don't know if that is a mistake yet. Will be getting the second battery in Feb so close to 30kw. Will buy one battery every year till I have 5. I can burn through 100kwh on a hot AZ Summer day. I am not even trying to run my house, just keep my hard earned Frankie's out of APS hands.
Once they figure out bidirectional EV chargers then my problems go away as I will have 100kw sitting in the garage that I can drive.

Wish there was an EG4 firmware guru somewhere I can bounce my ideas off of. After 3 days working with SS and EG4 this is what I got
How can I discharge 121w into nothing and have zero watts feeding my house from 4pm till now...sad. anyone know what backup power ESP even is?

Screenshot_20240123-192011~2.png
 
Yep this was a tough week to start my system. Had a solaredge without battery for 5 years. Designed all my solar systems and picked EG4 on price since the savings over solark covered the first 14kw battery, don't know if that is a mistake yet. Will be getting the second battery in Feb so close to 30kw. Will buy one battery every year till I have 5. I can burn through 100kwh on a hot AZ Summer day. I am not even trying to run my house, just keep my hard earned Frankie's out of APS hands.
Once they figure out bidirectional EV chargers then my problems go away as I will have 100kw sitting in the garage that I can drive.

Wish there was an EG4 firmware guru somewhere I can bounce my ideas off of. After 3 days working with SS and EG4 this is what I got
How can I discharge 121w into nothing and have zero watts feeding my house from 4pm till now...sad. anyone know what backup power ESP even is?

Yep this was a tough week to start my system. Had a solaredge without battery for 5 years. Designed all my solar systems and picked EG4 on price since the savings over solark covered the first 14kw battery, don't know if that is a mistake yet. Will be getting the second battery in Feb so close to 30kw. Will buy one battery every year till I have 5. I can burn through 100kwh on a hot AZ Summer day. I am not even trying to run my house, just keep my hard earned Frankie's out of APS hands.
Once they figure out bidirectional EV chargers then my problems go away as I will have 100kw sitting in the garage that I can drive.

Wish there was an EG4 firmware guru somewhere I can bounce my ideas off of. After 3 days working with SS and EG4 this is what I got
How can I discharge 121w into nothing and have zero watts feeding my house from 4pm till now...sad. anyone know what backup power ESP even is?

View attachment 190994
Where are your CTs? Do you have any install pictures/diagrams?
 
Where are your CTs? Do you have any install pictures/diagrams?
I have a SPAN panel with an outside meter pan. CT's are on the load side tap with arrows pointing to the inverter. Before today's trip to tech support hell everything was working but we could not get the battery to feed the load independently of the grid from 4-7. The only change they made was to sync the clock to AZ time since it was screwed up and turn on grid peak shaving and some switch that stops all export to the grid.
What picture do you want to see, all the wiring is pretty normal, I don't have anything tied to the load terminals as I am not trying to feed a CLP at this time. The SPAN panel will do that eventually...hopefully! I have the EG4 wall mount battery so comms should be OK. Really I am not asking this system to do anything crazy, so if two tech support groups don't figure this out quickly then I made a costly mistake. My buddy put in a solark at my recommendation with zero issues doing exactly what I want to do, I just cheaped out unfortunately.
 
I have a SPAN panel with an outside meter pan. CT's are on the load side tap with arrows pointing to the inverter. Before today's trip to tech support hell everything was working but we could not get the battery to feed the load independently of the grid from 4-7. The only change they made was to sync the clock to AZ time since it was screwed up and turn on grid peak shaving and some switch that stops all export to the grid.
What picture do you want to see, all the wiring is pretty normal, I don't have anything tied to the load terminals as I am not trying to feed a CLP at this time. The SPAN panel will do that eventually...hopefully! I have the EG4 wall mount battery so comms should be OK. Really I am not asking this system to do anything crazy, so if two tech support groups don't figure this out quickly then I made a costly mistake. My buddy put in a solark at my recommendation with zero issues doing exactly what I want to do, I just cheaped out unfortunately.
Here is a shot of it working but not when I want it to, it was charging the battery and feeding my loads. Then at 4pm it stopped doing anything normal. I am even considering infant mortality. They have upgraded my firmware 2 times already and that's usually not a good sign eitherScreenshot_20240120-185628~2.png
 
Yep this was a tough week to start my system. Had a solaredge without battery for 5 years. Designed all my solar systems and picked EG4 on price since the savings over solark covered the first 14kw battery, don't know if that is a mistake yet. Will be getting the second battery in Feb so close to 30kw. Will buy one battery every year till I have 5. I can burn through 100kwh on a hot AZ Summer day. I am not even trying to run my house, just keep my hard earned Frankie's out of APS hands.
Once they figure out bidirectional EV chargers then my problems go away as I will have 100kw sitting in the garage that I can drive.

Wish there was an EG4 firmware guru somewhere I can bounce my ideas off of. After 3 days working with SS and EG4 this is what I got
How can I discharge 121w into nothing and have zero watts feeding my house from 4pm till now...sad. anyone know what backup power ESP even is?


My unit runs with EPS on all the time. I think this is the power out to the "load" lugs, and leech. I think it stands for "Emergency Power". I just turned EPS back on this evening after my batteries charged to 100%. It's been off for over two days. No sun no battery charging. Might make it thru tomorrow with the bat's and a modicum of sunlight.

1706074502008.png


I'm paralle (2)l, I run everything from a bus off the load lugs, no flow from/to the grid, but I have it connected with a small breaker to only one inverter for phase sync. When I want to disable output but allow the batteries to charge I tap the 'Power Backup' to 'Disable'. This shuts off the 'EPS' output. Again I'm not in off-grid mode, I just let the unit think the grid is not working properly (only connected to one inverter) so it syncs the phases for the sine wave, (tested with o-scope) but does not appear to otherwise do anything with the grid connections. Thus when the ATS clicks it is not a violent transition (which it was 1/2 the time prior).


1706074617931.png

If I understand it the output settings are here: You should be able to set Forced Discharge for your TOU (4-7). Assuming EG4 batteries you should be able to set your "On-Grid" settings as well. My assumption would be if you set control to SOC and cutoff to 50% it would start dumping batteries to grid. Might be wrong. The other assumption is that this may require forced, thus enable this and set the stop to say 30% (assuming it's a tiered approach) and then set a start/stop time. I would start by simply enabling forced and leaving the times all zero's I would think this would be blanket, but I'd play with it.


1706074741081.png

Me? I just let the inverter turn off when SOC is 10%, but I think forced discharge is what you want for TOU shifting. Clear as mud in the manuals IMNSHO. Did you download the latest manual? The current rev is like 2.1.

Good Luck!
 
My unit runs with EPS on all the time. I think this is the power out to the "load" lugs, and leech. I think it stands for "Emergency Power". I just turned EPS back on this evening after my batteries charged to 100%. It's been off for over two days. No sun no battery charging. Might make it thru tomorrow with the bat's and a modicum of sunlight.

View attachment 191001


I'm paralle (2)l, I run everything from a bus off the load lugs, no flow from/to the grid, but I have it connected with a small breaker to only one inverter for phase sync. When I want to disable output but allow the batteries to charge I tap the 'Power Backup' to 'Disable'. This shuts off the 'EPS' output. Again I'm not in off-grid mode, I just let the unit think the grid is not working properly (only connected to one inverter) so it syncs the phases for the sine wave, (tested with o-scope) but does not appear to otherwise do anything with the grid connections. Thus when the ATS clicks it is not a violent transition (which it was 1/2 the time prior).


View attachment 191002

If I understand it the output settings are here: You should be able to set Forced Discharge for your TOU (4-7). Assuming EG4 batteries you should be able to set your "On-Grid" settings as well. My assumption would be if you set control to SOC and cutoff to 50% it would start dumping batteries to grid. Might be wrong. The other assumption is that this may require forced, thus enable this and set the stop to say 30% (assuming it's a tiered approach) and then set a start/stop time. I would start by simply enabling forced and leaving the times all zero's I would think this would be blanket, but I'd play with it.


View attachment 191003

Me? I just let the inverter turn off when SOC is 10%, but I think forced discharge is what you want for TOU shifting. Clear as mud in the manuals IMNSHO. Did you download the latest manual? The current rev is like 2.1.

Good Luck!
I was told to not use forced discharge, did try it one it just dumps its load to the grid no matter what the house load is. I had it set for 10kw, that was exciting. I think you are correct it has something to do with the grid vs no grid enable and to disable EPS. Going to talk to EG4 today. its sill locked in this EPS mode, I have not connections to the load lugs so its feeding zero yet it found a way to discharge 10% of the battery to nothing during the night.
The software is so some degree not ready for prime time and I can't find the software expert in either organizations right now that fully understands it and what I need to do. Wanting to feed my loads during peak rates is not complicated at all, it should be obvious but the app is not obvious. I have 2 versions of the manual, its 2.1
 
I appreciate your help, are you in AZ. Are you ongrid and trying to avoid the peak load rates and peak load max Kwh tax
 
I appreciate your help, are you in AZ. Are you ongrid and trying to avoid the peak load rates and peak load max Kwh tax
EG4 asked that I not change the setting they made as they collect data
to me what I am asking the system to do is elementary and what most people would want. My friend has the Solark and it was up and running in one day perfecly. Again seem the EG4 software is not ready for prime time. I will suffer one more day using full APS rates as right nowScreenshot 2024-01-24 091920.jpg my inverter and feeding a fantom load called EPS and my solare is feeding both the battery and EPS with zero of my solar going into the house....completely unacceptable
 
Everything is now working as designed and per my requirement. Took some time and EG4 tech support. it does appear I don't have full access to the firmware so I am working on that too as I need to make annual changes to adopt to rate changes. Its a work in progress
 
This is an offgrid design I recently helped someone do:

View attachment 161427
I have pretty much this setup but I don't have battery comms yet. I can't seem to get it to turn on the inverter, though the system powers up. I've set the control to be Voltage instead of SOC, of course, but I don't get a battery voltage showing up on the dashboard either.

Any thoughts for getting this to turn on the inverter? I'm just configuring via screen for now, no internet available unless I set up my phone for it, which I guess I could do. I also don't really want to get involved in their cloud app to configure it.
 
@Markus_EG4 can you detail how to do this? Who does the "unlocking". I have been asking EG4 for a while to do this exact task. I have to change my settings 2 times a year to keep up with the charges of my local utility. Right now I don't even know what EG4 did during commissioning to make my 18k PV inverter work perfectly, but in May I have to change the settings. I need to download the existing setpoints and also know where the changes would be made. The firmware for the PC app, cell app, and inverter screen all appear to have a different level of detail and the manual does not match all of them at this point. Also I second the motion to be able to save a firmware file and be able to upload it if anything happens or like me you just want to make annual changes.
 
@Markus_EG4 can you detail how to do this? Who does the "unlocking". I have been asking EG4 for a while to do this exact task. I have to change my settings 2 times a year to keep up with the charges of my local utility. Right now I don't even know what EG4 did during commissioning to make my 18k PV inverter work perfectly, but in May I have to change the settings. I need to download the existing setpoints and also know where the changes would be made. The firmware for the PC app, cell app, and inverter screen all appear to have a different level of detail and the manual does not match all of them at this point. Also I second the motion to be able to save a firmware file and be able to upload it if anything happens or like me you just want to make annual changes.
This would indeed be VERY helpful! @Markus_EG4
 
Hi! What are your feelings about skipping the Solar Disconnect and using the On/Off switch on the side of the 18K. Using that, instead of the IMO 8 Pole Switch. Any ideas on pro's and cons? The one thing I'd note is I'm using a combiner box on the roof, so I can disconnect power there if I need to work on the lines between the panels and the inverter, I can cut the power there. Thoughts?
This is what my system does- one 18kPV inverter, 2 powerpro batteries, whole house just like Filterguy but I have no PV disconnects, just a remote RSD switch by the main panel and next to the PG&E meter approx 70 ft away from my inverter/battery room and i just received my final inspection today! YAY!!
 