Amps +-
Hello
I am using a Schneider AGS with a XW Pro system. The AGS is connected to a diesel generator with a factory 2 wire auto start, this is wired using the type 14 wiring style as instructed in the AGS Manual.
I have programed the Gen warmup cycle to 300 seconds(5 minutes) on insight local.
The problem is I get no warmup cycle, the generator starts, immediately qualifies and starts charging.
The generator cool down cycle does work, it disconnects from power and let's the generator cool down for the programed cool down time.
Is Anyone else using this combination?