They are 10k eachI'd do option 1 but 50amp breaker, aren't they 5k watts each?
They are 10k eachI'd do option 1 but 50amp breaker, aren't they 5k watts each?
Or could you put both units in split phase output, and then feed a 200 amp panel with a 60 amp 2 pole breaker from each inverter?Thinking ahead.
How would everyone go about wiring them up in parallel?
Option 1 - 6 AWG from each inverter to a double pole 60A breaker with L1's to one side of the bus and L2's to the other.
Option 2 - 6 AWG from each inverter to a power distribution block (I think that's what they are called, Engineer775 uses them in lots of his installs) then 2 AWG to a double pole 100A breaker.
I think option 1 would be "safer" but option 2 would make wiring easier.
I don't think I'll be connecting them to the grid at all, double conversation for grid charging with rectifiers if/when needed and use the inputs for the generator. My logic for this is I'm planning further ahead for my completely off grid setup someday (hopefully sooner than later).
View attachment 212125
each leg isn't 10k, the whole unit is 10k. you mean 5k each.. hence 50amp breakerThey are 10k each
I meant each unit is 10k. I interpreted your 5k each as per invertereach leg isn't 10k, the whole unit is 10k. you mean 5k each.. hence 50amp breaker
You don't use 1 breaker across the whole unit
Are they telling you to put your neutral on a breaker?
Yea, I should have expanded on my thoughts further. I'm going to run them into a dedicated "inverter" panel then feed the house panels from the inverter panel. I figure this will make it easier to add more, not that I'll ever need them; yet.Or could you put both units in split phase output, and then feed a 200 amp panel with a 60 amp 2 pole breaker from each inverter?
I have no plans to.Are they telling you to put your neutral on a breaker?
Wasn't getting baba notifications.
Attached is the proforma invoice.
It will be ~$2300, after the baba fees for using a CC, for 2 ASP 10kW shipped air freight, DDP...
Wasn't getting baba notifications.
Attached is the proforma invoice.
It will be ~$2300, after the baba fees for using a CC, for 2 ASP 10kW shipped air freight, DDP...
Depends, what is SRNE reputation for reliability, customer service and warranty? If you're relying on it to keep the lights on and the meat in the deep freezer good do you really want the cheapest option? I've never looked into SRNE so I don't know their history, if they can provide a comparable product to midnite, Schneider and solark then sure I can see this causing a disturbance in the force.I chatted with an Ebay seller who is selling the ASP SRNE and they seem to do a lot of installation business. I get the impression they are actively installing the ASP inverters right now. I think this inverter is going to cause other sellers such as Midnite, etc to rethink their pricing. 20kw for $2300 is a game changer. The top tier guys want $10000 to get 20kw. What a mismatch!
Originally I posted to combine using a distribution block or Polaris type connector, however looking at the diagram, each inverter feeds a 120V leg similar to Voltronic inverters in parallel.Thinking ahead.
How would everyone go about wiring them up in parallel?
Option 2 - 6 AWG from each inverter to a power distribution block (I think that's what they are called, Engineer775 uses them in lots of his installs) then 2 AWG to a double pole 100A breaker.
Look at the diagram again, it appears each inverter supplies one leg, not both.each leg isn't 10k, the whole unit is 10k. you mean 5k each.. hence 50amp breaker
You don't use 1 breaker across the whole unit
Where did you get this? That would be 7.5Kw per leg?
Need some clarification on these diagrams. The big one in the post I believe is for 230V Euro.Thinking ahead.
How would everyone go about wiring them up in parallel?
Option 1 - 6 AWG from each inverter to a double pole 60A breaker with L1's to one side of the bus and L2's to the other.
Option 2 - 6 AWG from each inverter to a power distribution block (I think that's what they are called, Engineer775 uses them in lots of his installs) then 2 AWG to a double pole 100A breaker.
I think option 1 would be "safer" but option 2 would make wiring easier.
I don't think I'll be connecting them to the grid at all, double conversation for grid charging with rectifiers if/when needed and use the inputs for the generator. My logic for this is I'm planning further ahead for my completely off grid setup someday (hopefully sooner than later).
View attachment 212125
Midnite DIY AIO's are SRNE. Schneider is not Chinese sourced but Sol-Ark is.Depends, what is SRNE reputation for reliability, customer service and warranty? If you're relying on it to keep the lights on and the meat in the deep freezer good do you really want the cheapest option? I've never looked into SRNE so I don't know their history, if they can provide a comparable product to midnite, Schneider and solark then sure I can see this causing a disturbance in the force.
Look at the diagram again, it appears each inverter supplies one leg, not both.
Not sure if this is 10Kw per 120V leg.
Where did you get this? That would be 7.5Kw per leg?
Absolutely not.Are they telling you to put your neutral on a breaker?
This is a good questionI sent a message to SRNE support asking what the rated output is for 2 units in parallel. Will update when I hear back.
Thanks. That's the same diagram (except the color) that I posted, isn't it?This is correct split phase diagram. Use either junction blocks or Polaris type connectors. 4 AWG or larger will suffice.