WHY do all-in-one Solar Power Inverters have a high idle consumption? Asking to learn...

I think 7 watts is possible, and if so that is damn good. My Renogy 12V 2000W HF inverter idles at .9a 13V = 12 watts. Same for the Renogy 12V 3000W HF. The Renogy 12V 3000W LF with fan on idles at 2.23A 13.1V = 29 and fan off is 1.67A 13.1V = 20 Watts.

The LF inverter also has grid charging and auto transfer capabilities that these HF inverters do not. That is valuable feature you get for the extra watts.

The question is, do we have to pay that 20W of overhead once a load kicks in? I tested a 250W heat lamp that draws exactly 250W on grid power and 258W on inverter due to higher AC voltage. When running on the inverter I get 21.9A 12.57V (small test battery) = 275 Watts. So the inverter is 93% efficient in this case and that includes the 20W of overhead power. In other words, when you have a substantial load, that standby power gets rolled into normal DC to AC inverter losses.
I think you have it most of the way, but standby power is exactly that, standby power. As soon as you add a 1w load, its no longer standby, its efficiency loss. The efficiency loss is much much greater at lower loads. If your inverter has a 50w standby, and you add a 50w load, the inverter is technically just 50% efficient.
 
What about multiphase/parallel systems? What's the point of diminishing returns? Is it better to get a 15kW 3-phase AIO or connect 3x 5kW AIOs together?
 
What about multiphase/parallel systems? What's the point of diminishing returns? Is it better to get a 15kW 3-phase AIO or connect 3x 5kW AIOs together?
i only know tiny amount here and i'm hoping to find a complete list of idle and power saving watt use for all units and "gotchas" for example, the growatt 3000 says: "Power saving function will be automatically disabled when in parallel operation." this might be standard i don't know? so for your question about parallel systems a single split-phase might use less power than two smaller units setup for split-phase?
 
My 3.6kw SMG II is not that bad , pretty sure its under 50w , haven't measured it exactly with amp meter to be honest but I can see the diagrams.

Rough calculation gives me around 35w ?

I think that's great no ? Or thats considered a lot here ?

Yes the best 3kw victors have like 15w but most are just the inverter , its not MPPT and it doesnt have a screen and 2xfans .

So my EASUN SMG II cheap 400$ all in one is not that far from one of the best inverters in the world ( victron ).

Am I missing something ?
 