The 5kw Sunsynk inverter manual states battery cable must be AWG2 35mm2, but the connectors on the Sunsynk battery are for AWG4 25mm2 cables, ok it is what it is.
AWG4 25mm2 cable connector is 100a max so it would be prudent to wire it as per the picture on the right.
The manual states 150a breaker - fuse, but as the batteries max charge rate is 100a shouldn't I use two 100a breakers? After all what is 150a breaker going to protect? Not the battery or the cable.
The inverters max charge rate is 120a, but I'll stick to the recommended 50a; but shouldn't the inverter be set for 100a as there are two batteries, giving 50a to each battery? Or am I over thinking this, and the inverter takes care of all that if set at 50a? I've not had chance to investigate the menu system yet.
I'm sorry to keep asking stupid questions but it's expensive kit, and sunsynk instructions contradict them selves. And sunsynk don't reply with any usable information, if at all.